mike93lx
ALLIANCE MEMBER
I am hoping to build a workshop next year and am trying to sort out the electrical. 60A will be plenty.
I want to locate my 30A/240V portable generator input at the workshop (would connect back to the main panel in the house on a proper disconnect).
the wiring would run for about 60ft inside the house and then will be underground for about 40ft to the shop.
if i ran this in the same conduit at any point, I would be subject to derating, correct? realistically, the shop would not be getting used in a power outage, which are incredibly rare anyway, but i recognize that code doesn't care about my personal situation.
Outside of derating, are there any prohibitions to this setup?
As the exterior run is so short, I'd probably run separate conduits anyway, but am curious about the options. If separate, likely 1.25" for 2-2-2-4 AL XHHW and 3/4" for 10-10-10-10 Cu THWN, if combined a single 1.5" would probably be fine. I do not need any network/cable out there.
I want to locate my 30A/240V portable generator input at the workshop (would connect back to the main panel in the house on a proper disconnect).
the wiring would run for about 60ft inside the house and then will be underground for about 40ft to the shop.
if i ran this in the same conduit at any point, I would be subject to derating, correct? realistically, the shop would not be getting used in a power outage, which are incredibly rare anyway, but i recognize that code doesn't care about my personal situation.
Outside of derating, are there any prohibitions to this setup?
As the exterior run is so short, I'd probably run separate conduits anyway, but am curious about the options. If separate, likely 1.25" for 2-2-2-4 AL XHHW and 3/4" for 10-10-10-10 Cu THWN, if combined a single 1.5" would probably be fine. I do not need any network/cable out there.