Quick question on wire and breaker size.

Using 2" conduit for entire run from main panel on side of house to sub panel in the garage I'll have roughly 135' to 140' of cable. 2-2-2-4 is readily available in my area.

Would like to go 90 amp breaker, at this distance should the cable be up-sized? or settle for a smaller breaker size?
 
To avoid these ads, REGISTER NOW!

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
Is that AL or CU?

CU looks like you are good for 90.

AL you can run 75

And of course what you SHOULD do depends entirely on HOW MUCH POWER YOU REALLY NEED IN THE GARAGE.

;)
 
OP
K

kest874

Active member
Joined
Mar 18, 2016
Messages
37
Location
Murfreesboro, TN
Aluminum, mostly wood working but not running a bunch simultaneously. Table saw (240 20 amp) dust collector window a/c unit at most.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,013
Location
Modesto, CA
I havent done the load calcs but at 140' with #2 al, 90a load could push the voltage drop past 3%.

But i doubt your load would ever be that high...

Make sure to isolate the neutral bus in your subpanel which usually means buying a separate ground bar. you will also need 2 ground rods...
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I usually put a 60 cause they off the shelf cheap. I have wired a couple dozen garages, NEVER had one call me back about a trip.
 
OP
K

kest874

Active member
Joined
Mar 18, 2016
Messages
37
Location
Murfreesboro, TN
I havent done the load calcs but at 140' with #2 al, 90a load could push the voltage drop past 3%.

But i doubt your load would ever be that high...

Make sure to isolate the neutral bus in your subpanel which usually means buying a separate ground bar. you will also need 2 ground rods...

Thanks everyone. Home Depot near me sells the 60 amp and 70 amp breakers on the shelf.

Running 2-2-2-4 mhf with 60 or 70 amp breaker instead of 2/0-2/0-1-4 MHF and 90 amp breaker would save me about $120.

In the GE panel (same brand as the main panel at the house) I'm using I removed the bond between the 2 neutral bars and installed the green bond screw where the grounds will land.

I have 2 8' copper-cad ground rods driven 8' apart connected with #6 CU.

I'm renting a trencher this weekend and installing the 2" inch conduit. I'll measure the feeder run after the conduit install to make sure I'm not over stepping.

Load calc I can't see using more than 35 to 40 amps at once. If I choose to get a welder in the future I can always pull new feeders then if needed.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,013
Location
Modesto, CA
Thanks everyone. Home Depot near me sells the 60 amp and 70 amp breakers on the shelf.

Running 2-2-2-4 mhf with 60 or 70 amp breaker instead of 2/0-2/0-1-4 MHF and 90 amp breaker would save me about $120.

In the GE panel (same brand as the main panel at the house) I'm using I removed the bond between the 2 neutral bars and installed the green bond screw where the grounds will land.

I have 2 8' copper-cad ground rods driven 8' apart connected with #6 CU.

I'm renting a trencher this weekend and installing the 2" inch conduit. I'll measure the feeder run after the conduit install to make sure I'm not over stepping.

Load calc I can't see using more than 35 to 40 amps at once. If I choose to get a welder in the future I can always pull new feeders then if needed.

I would check to make sure those are listed to be used like that. Often times they are not and a separate ground bar kit is required.

I prefer to have a neutral bar and ground bar on each side to keep the wiring tidy and prevent wires crisscrossing the panel.
 
OP
K

kest874

Active member
Joined
Mar 18, 2016
Messages
37
Location
Murfreesboro, TN
I would check to make sure those are listed to be used like that. Often times they are not and a separate ground bar kit is required.

I prefer to have a neutral bar and ground bar on each side to keep the wiring tidy and prevent wires crisscrossing the panel.

Thanks, I'll check that out it's a GE TM3220CCU and I do find ground bar kits available for it. Would definitely make it tidy and easier to work on.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,754
To those who are suggesting a 75A breaker there is no such beast, only 70A or 80A there is price jump going from 60A to 70A, and then another jump in price going for a 80A.
 
OP
K

kest874

Active member
Joined
Mar 18, 2016
Messages
37
Location
Murfreesboro, TN
To those who are suggesting a 75A breaker there is no such beast, only 70A or 80A there is price jump going from 60A to 70A, and then another jump in price going for a 80A.


Believe the 75 comes from the voltage drop calculator. 60 amp = $10 7 amp = $32 at local Home Depot
 
OP
K

kest874

Active member
Joined
Mar 18, 2016
Messages
37
Location
Murfreesboro, TN
Attached picture of main panel above, note the ground kit holes on the right. the area I marked red is the bond I removed. red arrow is where the green bond screw was inserted.

Doesn't appear to be ground bar kit installation holes on the left side would you drill and thread some or would you omit that ground bar on the left and still remove the bond landing neutrals on the right side with a ground kit installed as well on that side?


I have 10 or so circuits planned out, this is a 32 space 40 circuit panel.
 