Curious to know how to make a surface mounted run of a 240v 50A #6 wire to get around this I-Beam. Line will enter at house wall seen in the top-right of image and include an outlet box before passing around the I-beam for another 20 feet to a final outlet box.
This is in the garage of a raised ranch home with garage integrated into the house (a bedroom above). Could possibly route into garage ceiling, but this would expose unseen cable to puncture from below.
Circuit will manage a 5,000 Watt / 21A shop heater plus, for now, a 15A 5HP 20 gallon air compressor, with a 23A larger compressor in mind later to replace it.
House is 200A and 60A breaker will be in a 100 sub-panel inside the garage/shop
I am just not experienced working with BX/Ac or conduit to know how to plan curves or "T's" etc.

Thanks for your comments
This is in the garage of a raised ranch home with garage integrated into the house (a bedroom above). Could possibly route into garage ceiling, but this would expose unseen cable to puncture from below.
Circuit will manage a 5,000 Watt / 21A shop heater plus, for now, a 15A 5HP 20 gallon air compressor, with a 23A larger compressor in mind later to replace it.
House is 200A and 60A breaker will be in a 100 sub-panel inside the garage/shop
I am just not experienced working with BX/Ac or conduit to know how to plan curves or "T's" etc.

Thanks for your comments