Hi all.

The water that drains out of the furnace is draining under the floor and not into the drain. It runs on top of the drain and then goes under the floor. What’s the best way to fix this?
 
To avoid these ads, REGISTER NOW!
OP
I

ive

Well-known member
Joined
Mar 8, 2011
Messages
1,533
Location
Canada
Picture
 

Attachments

  • D3E5DF43-4FA6-4787-8ED2-E6C9E408C2DF.jpg
    D3E5DF43-4FA6-4787-8ED2-E6C9E408C2DF.jpg
    100 KB · Views: 131

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,777
Location
Long Island
Open up the floor around that iron drain cap so you can pull the cover off, and then replace the cover with one that has a recessed center.
 
OP
I

ive

Well-known member
Joined
Mar 8, 2011
Messages
1,533
Location
Canada
Hi. Thanks for the idea. Maybe drill the cover to take the fitting?
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,777
Location
Long Island
Hi. Thanks for the idea. Maybe drill the cover to take the fitting?

That could also work. A step drill bit (I suggest the HF one) can be used to open up an existing hole to the diameter you require. The elbow approach will prevent water coming from the condensate lines from getting under the floor, but will not help with water poured in that drain from a bucket.

There should be some sort of "air break" betweecondensate drain line and floor drain.

There needs to be an air gap between the highest possible water level in the trap below that cover and whatever fitting you install. Basically, don't put anything in to extend the elbow downwards.

And a condensate neutralizer on the drain line.

Tommy

Agreed, there should be a condensate neutralizer. I prefer clear ones where you can easily see if they need to be refilled.
 
OP
I

ive

Well-known member
Joined
Mar 8, 2011
Messages
1,533
Location
Canada
Thanks guys. Will send a pic when I’m done if it looks nice :)
 
To avoid these ads, REGISTER NOW!

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,436
Location
N CA
I hope the drain line is plastic. The pH on gas fired condensate is about 3.2. A cast iron or steel line which sees only condensate will not last. Also, concrete being a lime based product, and limestone being what you put into the condensate neutralizing trap you should build, it will quickly eat the slab. Back in the late 80's I had a guy buy a furnace I represented and used it for a construction heater over the winter. He did put a supply plenum on top and strapped that to the floor joists in the basement. He called me in the spring demanding a new furnace under warranty. He had let the condensate run onto the floor all winter. That unit has a 12 ga base plate under it and it and the bottom 2-4" of the furnace were gone. What was left was suspended and his slab in about a 6'radius was a bunch of polished aggregate and only about 2" of concrete left. I tell ya. You just can't dream this stuff up;)
 
OP
I

ive

Well-known member
Joined
Mar 8, 2011
Messages
1,533
Location
Canada
Hi guys.

I attempted to resolve this today. I wanted to just add some 90* fittings amd drill the cover. The problem I ran into was that the line on the condensate exhaust doesn’t fit the pvc fittings I bought. The od of the exhaust line is 7/8’s. I’ll post a pic
 
OP
I

ive

Well-known member
Joined
Mar 8, 2011
Messages
1,533
Location
Canada
I need to add a coupling as well. The hvac guys made the line just a little short. Anyways these fittings won’t work.


What am I doing wrong?
 

Attachments

  • D8D5C1E5-50D9-47E2-B5A8-87731922E731.jpg
    D8D5C1E5-50D9-47E2-B5A8-87731922E731.jpg
    155 KB · Views: 47

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,372
Location
Michigan
Look and see if the pipe you have is pvc or cpvc, the sizes are different so you have to have the same type of pipe. Your pipe may say 1/2" or 3/4" pvc, if so buy that size fitting. It looks to me like you have cpvc fittings as they are a bit off white instead of plain white.

Sent from my SM-G965U using Tapatalk
 

BD1

Well-known member
Joined
Mar 18, 2007
Messages
4,602
Location
north side
If you bought PVC and it doesn't fit, then it's CPVC.
Buy a coupling to go on the existing short pipe, then buy a STREET elbow. The pipe size end will go into the coupling. This maybe long enough to avoid buying any pipe. Make hole in drain so elbow fits in.
You can add tywraps to hold to drain cover.


Sent from my iPhone using Tapatalk
 

welder4956

Well-known member
Joined
Apr 8, 2010
Messages
3,111
Location
Birmingham, AL USA
Hi guys.

I attempted to resolve this today. I wanted to just add some 90* fittings amd drill the cover. The problem I ran into was that the line on the condensate exhaust doesn’t fit the pvc fittings I bought. The od of the exhaust line is 7/8’s. I’ll post a pic

1/2" PVC pipe O.D. is 0.840", which is slightly under 7/8" (0.875"). If you bought 3/4" fittings you got the wrong size.
 

SALIV8

Well-known member
Joined
Dec 11, 2008
Messages
2,114
Location
chicago and s/w michigan
I would just grab proper size 45*, push fit only and keep it resting against the floor drain just touching. Almost a horizontal position. Wouldn’t even need to remove tie wrap and no drilling.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
1/2" PVC pipe O.D. is 0.840", which is slightly under 7/8" (0.875"). If you bought 3/4" fittings you got the wrong size.

If he has a 1/2" condensate line, they installed the wrong size. Condensate lines have to be 3/4" minimum by code.