So - went to my nieces house today to troubleshoot a problem with her new Ring 2 doorbell that my brother installed for her. Problem was that once the doorbell was pressed the chime inside the house would not stop ringing.
First thing I did was pull the chime from the wall - it was recessed into the wall in the hallway in basically a two gang box with a divider in the middle. One side had the AC input - the other side had the line going to the actual doorbell.
Problem is, the output voltage was 12V DC - the Ring requires AC voltage. The fix is fairly easy since I have 120 right there in the box - install a transformer in the current box and put a new chime over the box.
My question is - I know transformers generate heat - is there any issue with putting the transformer in the side of the box with the AC in - essentially a single gang box? Then covering it with the door chime? I know they are sometimes installed in a junction box in the attic but inside a wall I'm not sure of.
First thing I did was pull the chime from the wall - it was recessed into the wall in the hallway in basically a two gang box with a divider in the middle. One side had the AC input - the other side had the line going to the actual doorbell.
Problem is, the output voltage was 12V DC - the Ring requires AC voltage. The fix is fairly easy since I have 120 right there in the box - install a transformer in the current box and put a new chime over the box.
My question is - I know transformers generate heat - is there any issue with putting the transformer in the side of the box with the AC in - essentially a single gang box? Then covering it with the door chime? I know they are sometimes installed in a junction box in the attic but inside a wall I'm not sure of.