Flexible conduit

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,948
Location
New England
I’m using 3/4 type rw flexible conduit to go from compressor to shut off box. I have two questions.
- my cutter does not go this big. Just use hacksaw?
- smaller mc like this has red bushings. This did not have them nor do the ones I saw at the store fit. Is there something that has to be done to protect the wires?


Sent from my iPhone using The Garage Journal mobile app
 
To avoid these ads, REGISTER NOW!

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
Hacksaw should work fine. Cut-off wheel works well too.

The red anti-short bushings are only required for AC cable. They're not required for MC cable or for flex conduit, but you can use them anyway. You shouldn't have to do anything special with the ends, just use the proper fittings for flex conduit.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,776
Location
NW Iowa
Commonly just called flexible metal conduit. I usually just kink it and cut with dikes. There is a cutter made for it, hacksaw will work too.

Just use the connectors made for it. You don't need anti-shorts for anything but AC cable. Even MC does not require them.
 

mobiledynamics

Well-known member
Joined
Mar 14, 2010
Messages
5,052
Location
Gotham City
? - ?

3/4 bushings do exist, and unless I've been doing it all wrong, and flex metal conduit should have a bushing to keep the edge from the wire.
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
3/4" plastic bushings certainly exist, and you're free to use them to your hearts content, but code doesn't require them until your wire is #4 or larger.
 

mobiledynamics

Well-known member
Joined
Mar 14, 2010
Messages
5,052
Location
Gotham City
not a spark so don't know code...

I don't see why one would use them for 4 and larger but not smaller. abrasion is abrasion whether it's #10 or #4
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,593
Location
Fullerton, CA
The anti short bushings for AC cable fit under the armor.
They're available for flex too that fit under the armor, are comparatively rare, and are completely different from the bushings that are used on the end of fittings.

(I, just as Bert does, snap the armor but don't use dykes. I use tin snips)
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
I prefer the jake style fittings that screw into the flex, that way no worries about damaging insulation, or need for anti shorts/redheads.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,776
Location
NW Iowa
not a spark so don't know code...

I don't see why one would use them for 4 and larger but not smaller. abrasion is abrasion whether it's #10 or #4

It's more about the corner of the fitting pushing through the insulation if the wire makes a sharp turn. Small wires bend easier so it not an issue.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,776
Location
NW Iowa
3/4" plastic bushings certainly exist, and you're free to use them to your hearts content, but code doesn't require them until your wire is #4 or larger.

I believe we're talking about the anti short bushings that protect the wire from sharp edges of the sheath of AC cable. Not the thread on bushings that go on the end of threaded conduit or fittings.
 
To avoid these ads, REGISTER NOW!
OP
K

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,948
Location
New England
I believe we're talking about the anti short bushings that protect the wire from sharp edges of the sheath of AC cable. Not the thread on bushings that go on the end of threaded conduit or fittings.



Actually found them at hd tonight. Like red heads but bigger


Sent from my iPhone using Tapatalk
 

mobiledynamics

Well-known member
Joined
Mar 14, 2010
Messages
5,052
Location
Gotham City
There are the -screw in fittings- into FMC which should also alleviate the concern about what burrs may present on a nick as well, versus a standard exterior clamp. Regardless, I do treat the exposed edge as a concern for any wire size
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
I believe we're talking about the anti short bushings that protect the wire from sharp edges of the sheath of AC cable. Not the thread on bushings that go on the end of threaded conduit or fittings.

Ya, there seems to be some confusion here. OP says 3/4" flex and you re-stated that in post 3. But I think others started talking about red-heads for AC, but that's not what OP says he is using. But then he says he found them at HD and are just large red-heads. Sounds like there's a bushing product I'm completely unfamiliar with. Kaizen do you have a link or pic of these 3/4" red-heads?
 
OP
K

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,948
Location
New England
Ya, there seems to be some confusion here. OP says 3/4" flex and you re-stated that in post 3. But I think others started talking about red-heads for AC, but that's not what OP says he is using. But then he says he found them at HD and are just large red-heads. Sounds like there's a bushing product I'm completely unfamiliar with. Kaizen do you have a link or pic of these 3/4" red-heads?


https://www.homedepot.com/p/3-4-in-...MC-Anti-Short-Bushing-16-Pack-75404/100197535



Sent from my iPhone using Tapatalk
 
OP
K

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,948
Location
New England
Ya, there seems to be some confusion here. OP says 3/4" flex and you re-stated that in post 3. But I think others started talking about red-heads for AC, but that's not what OP says he is using. But then he says he found them at HD and are just large red-heads. Sounds like there's a bushing product I'm completely unfamiliar with. Kaizen do you have a link or pic of these 3/4" red-heads?



https://www.homedepot.com/p/3-4-in-...MC-Anti-Short-Bushing-16-Pack-75404/100197535


Sent from my iPhone using The Garage Journal mobile app
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
I'll be damned. Red-heads, just huge for conduit instead of AC cable. I've never seen such a thing. Learned something new.
 