My new next door neighbors went out of town for a few days so I let their chickens in and out for them everyday
I walk by the condenser going to the coup and noticed one of the units was frosted up
About that time the defrost cycle kicked in and cleared it up
Am I wrong to think low freon
This condenser unit was replaced by the previous owners roughly 3 years ago
c23b750072d1650da0bc735492b0be34.jpg



Sent from my iPhone using Tapatalk
 
To avoid these ads, REGISTER NOW!
OP
H

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
Jd
I like that
I’m a big fan of the Allman Brothers
I haven’t seen that before
 
To avoid these ads, REGISTER NOW!

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
That means their filter's clogged.

Yup. Know someone that had only clogged filters that iced it up like a brick


Sent from my iPhone using Tapatalk

That only happens on an A/C only evaporator. Being located in Virginia, I'm going to have to assume that picture shows the outdoor half of a heat pump. It's normal for heat pumps running in heat mode to ice up a little before going into defrost. What I don't get is the weird ice pattern. It should be even, not have gaps like that.