2 different circuits. All new wiring, new 15 amp circuit breakers. Both 14 gauge. Resting voltage is 123 volts measured with digital multimeter.
Receptacle on circuit 1 is 5 feet (5 ft of conductors) from the panel. With a heavy load (shop vac) running, the initial voltage drop on start-up is about 1 volt, from 123 volts down to 122, then it goes back up to 123 during normal operation.
Receptacle on circuit 2 is about 90 feet (90 feet of conductors) from the panel. With the same load, the initial voltage drop on start-up is about 16 volts, from 123 down to 107, then it goes up to 116 volts during normal operation.
The shop vac's initial startup draw is 22 amps. Running is 11 amps (normal as spec'd on the label). Measured with an analog amp clamp.
Are my voltage drops normal?
The reason I’m even measuring is because when there is a heavy load (power tool or vacuum, etc), the lights on that circuit dim greatly during the tool start-up. The circuit with the large voltage drop. The light basically shuts off for a split second.
The electric company already put 3 new connectors outside of the house. They said they will replace the transformer sometime soon because my house is the last house on the street.
We’ve already checked all connections at the panel and at the receptacles. No fix. So we tried an all new circuit. Still dims. I'm wondering if the long run is what is causing the dimming. The receptacle at 5ft doesnt dim. The receptacle at 90 ft dims.
Thank you.
Receptacle on circuit 1 is 5 feet (5 ft of conductors) from the panel. With a heavy load (shop vac) running, the initial voltage drop on start-up is about 1 volt, from 123 volts down to 122, then it goes back up to 123 during normal operation.
Receptacle on circuit 2 is about 90 feet (90 feet of conductors) from the panel. With the same load, the initial voltage drop on start-up is about 16 volts, from 123 down to 107, then it goes up to 116 volts during normal operation.
The shop vac's initial startup draw is 22 amps. Running is 11 amps (normal as spec'd on the label). Measured with an analog amp clamp.
Are my voltage drops normal?
The reason I’m even measuring is because when there is a heavy load (power tool or vacuum, etc), the lights on that circuit dim greatly during the tool start-up. The circuit with the large voltage drop. The light basically shuts off for a split second.
The electric company already put 3 new connectors outside of the house. They said they will replace the transformer sometime soon because my house is the last house on the street.
We’ve already checked all connections at the panel and at the receptacles. No fix. So we tried an all new circuit. Still dims. I'm wondering if the long run is what is causing the dimming. The receptacle at 5ft doesnt dim. The receptacle at 90 ft dims.
Thank you.