240 outlet - which one?

rd65

Well-known member
Joined
Sep 29, 2017
Messages
2,837
Location
Granite Falls, WA
I am going to install a 240 outlet in my shop. I don't currently have a need but am going to install one. I do have a dual voltage air compressor that is doing just fine on 120. My small mig is 120. What are the recommendations as far as amperage and outlet type. There seems to be many to choose from and as I don't have anything that uses this I don't know which one to put in. I did buy the pictured unit (per the guy at Lowes). I have some 8awg wire. Outlet will be less than 2' from panel.
 

Attachments

  • IMG_20200329_125744398.jpg
    IMG_20200329_125744398.jpg
    40.9 KB · Views: 43
To avoid these ads, REGISTER NOW!

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,612
Location
BC
Your picture is a dryer receptacle (14-30R). If you switch your compressor over to 240V, it will draw about half the amperage it did on 120V.

Sounds like all you need are 120v/20A receptacles for that equipment.

For 240V receptacles in my shop, I mainly use the 6-20R (240v/20A).

white-leviton-electrical-outlets-receptacles-r52-05821-0ws-64_1000.jpg


A 6-50R is most common for welders.
black-leviton-electrical-outlets-receptacles-r10-05374-s00-64_1000.jpg
 

Milton Shaw

Well-known member
Joined
Feb 11, 2011
Messages
4,850
That 6-20 R is almost the same as the 120 version and if you don't read the box you will get the wrong one. The difference is which pin is twisted. The plug on the 6-20 looks like the 120 volt 20 amp version and is very easy to confuse.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,073
Location
Modesto, CA
I am going to install a 240 outlet in my shop. I don't currently have a need but am going to install one. I do have a dual voltage air compressor that is doing just fine on 120. My small mig is 120. What are the recommendations as far as amperage and outlet type. There seems to be many to choose from and as I don't have anything that uses this I don't know which one to put in. I did buy the pictured unit (per the guy at Lowes). I have some 8awg wire. Outlet will be less than 2' from panel.

The problem with this thinking is whatever you buy may not work with the equipment you eventually buy.

the circuit is sized based on the equipment specs.

Since you dont have any equipment, you have no specs to go on.

Now the outlet you bought is useless for 240v equipment because the neutral is not needed. Not sure why the Lowes guy told you to get that one. If you did end using this with say a 240v motor, you would need a different plug than what would come with it since the neutral is unused

Since the panel is so easily accessible, why bother getting anything right now? Why are you bothering with this?
 

couch67

Well-known member
Joined
Mar 18, 2016
Messages
1,410
Location
Ontario Canada
future proofing for a 240v circuit is tough without knowing your future wants/needs. Are you closing in the walls, or can you do this later when its needed? You are only 2' from the panel so this should be easy to add later -

Edit: took waay too long to type, wylie beat me to it
 
Last edited:
To avoid these ads, REGISTER NOW!

bigmaq

Well-known member
Joined
Jul 31, 2019
Messages
65
Location
New York
Agree with Stuart. Just cap the wires and the box and leave it dead. Then when you have your equipment you can buy the appropriate outlet and cover size.
 
OP
R

rd65

Well-known member
Joined
Sep 29, 2017
Messages
2,837
Location
Granite Falls, WA
Mostly adding because I already have the box and conduit run. Nothing is in the walls. I was mainly wondering if there was a 'most' common outlet that was in use. My step son has a new Miller 120/240 welder that uses a 6/50R. He runs it in the house garage in his area running 120.
 
OP
R

rd65

Well-known member
Joined
Sep 29, 2017
Messages
2,837
Location
Granite Falls, WA
I know this is a loaded question but here it goes anyway. Is there a problem with running the 6-50 outlet with 8 gauge wire to a 40 amp breaker? Asking because I have 8 ga wire and the 40 amp breaker came with the panel.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
No problem. 40 is fine. I didn't catch that the 8 is in pipe, can use 50. 2 hots and ground for a welder. Many modern welders now allow 14 single circuit in pipe with 30 to the 50 welder outlet. If the wire is 12 or better up to 50.
No one thinks some of the minimums are a real great idea, I have wired some 12/30. Some of the outlets are not listed for wire that small and it does start to make v drop a factor. But the 8 is the ideal, will run anything with factory cord and plug to a smoking cinder.
 
Last edited:
OP
R

rd65

Well-known member
Joined
Sep 29, 2017
Messages
2,837
Location
Granite Falls, WA
No problem. 40 is fine. I didn't catch that the 8 is in pipe, can use 50. 2 hots and ground for a welder. Many modern welders now allow 14 single circuit in pipe with 30 to the 50 welder outlet. If the wire is 12 or better up to 50.
No one thinks some of the minimums are a real great idea, I have wired some 12/30. Some of the outlets are not listed for wire that small and it does start to make v drop a factor. But the 8 is the ideal, will run anything with factory cord and plug to a smoking cinder.
Cool, thanks for the feedback. Now to finding a time that I can get into a store to pick. We are on a bit of a lock down here in WA state.
 
OP
R

rd65

Well-known member
Joined
Sep 29, 2017
Messages
2,837
Location
Granite Falls, WA
Lowes was cool enough to let me return the wrong outlet & plug for store credit. After some searching I was able to locate the correct item. Really wish the labels would include info like 6-50R instead of making you search on the item through the bag.
Thanks for all the help.
 