Looking to buy a used 3ph baldor motor to hook up to a VFD for a machine build. Advertised as working, are there any things to be weary of buying a motor that was likely used in industry? Do nothing and send it? Replace bearing and send it? Thanks.
VFDs can be hard to the motor windings. Some folks have issues with older motors, so do not. New motors have "inverter rated" markings on the motor plate for VFD use. Or research the motor part number. Per the vfd entry on wikipedia:
Elevated-voltage stresses imposed on induction motors that are supplied by VFDs require that such motors be designed for definite-purpose inverter-fed duty in accordance with such requirements as Part 31 of NEMA Standard MG-1.
I've run motors from the ~1940s on VFDs and they seem just fine. Not for extended periods like fan duty but on and off for drilling holes and its all good.
VFDs can be hard to the motor windings. Some folks have issues with older motors, so do not. New motors have "inverter rated" markings on the motor plate for VFD use. Or research the motor part number. Per the vfd entry on wikipedia:
Elevated-voltage stresses imposed on induction motors that are supplied by VFDs require that such motors be designed for definite-purpose inverter-fed duty in accordance with such requirements as Part 31 of NEMA Standard MG-1.
open the peckerhead, take a whiff. burned is burned.
make sure the wires aren't stiff like theyve been overheated.
take a meter and ohm out phase to phase and phase (L1 to L2, L1 to L3, L2 to L3), they should be equal. also check phase to case ground and make sure it's completely open. you could put a megger on it to be sure the insulation is in good order as well if you wanted to go farther.
bearings are pretty much a lifetime thing. if a bearing went out, then it likely took the motor with it. just make sure they feel decent.
other than that, 3 phase are pretty simple.
what size motor was this going to be?
Great advice except for that last bit imo. Between the two of us, dad and I have replaced a pile of motor bearings.
just my experience working in industrial plants since i got out of the navy. rarely ever had to replace bearings because people let them go so long they toast the motor insulation while they overwork for months on end.
but yeah, you could easily replace bearings.
Chinese motors have a different stink. It's the varnish on the windings.Smell it. Burned windings stink. Pretty hard to miss.
VFDs do not shove higher voltage than normal. Motors tend to overheat when run on them because they are used to lower the frequency and therefor the rpm. Motors normally are cooled by moving air. Lower the speed and you have less air movement. That causes the motor to overheat. VFD rated motors are made more heat tolerant. In fact, Every VFD I have been aquainted with allows for soft start which lowers the stress on the motor.