Wiring shed main circuit panel

alex1988

New member
Joined
Jul 11, 2015
Messages
2
Want to move woodworking power tools from basement to 10x16 foot shed. Shed currently wired in a Connecting Box (not a Panel) via 2" underground #40 PVC to home 200 amp Main Panel with 125 feet of #4 THHN (4 wires including ground). This circuit connects my gasoline generator in the shed to the house when we lose power. Also in the conduit is a 20 amp circuit from the Main Panel to the to the shed for lighting and small power usages (3 wires including ground). I also have a 100 amp sub panel (Sub Panel #1) in the shop area of my basement - about 50 closer to the shed than the Main Panel.

Questions:
1) Is it permissible to feed Sub Panel #2 from existing Sub Panel #1?
2) Using Southwire's Conduit Fill Calculator using the existing Main Panel to shed 2" PVC #40 conduit, 4 wires of the existing #4 THHN wire, and 4 wires of new #6 THHN wire results in a Fill of 15.6% and a Very Low Jam Probability of 6.4%. My question is: Can I remove the existing #10 wire and pull through the new #6 wire without damaging the existing #4 wire? If that is not a wise choice, what are my options?
3) Is it realistic to pull all of the existing cable from the conduit to the shed, remove the #10 wire, and add the #6 wire and then pull the #4 & #6 back through, together?
4) Or, run a new 1" or 1.25" conduit from the Main Panel to the shed for Sub Panel #2 - I could run it side-by-side with the existing 2" conduit. The new Sub Panel #2 will be in a different location than the existing Connection Box in the shed so two conduits would be no problem from a wiring standpoint.

The new Sub Panel will have a 60 amp Main Breaker and grounded with (2) 8 foot grounding rods outside the shed.

Sorry for so many questions but I really want to know what I am talking about before going to my regular electrician.

Many thanks!
Bob
 
Last edited:
To avoid these ads, REGISTER NOW!

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
I couldn't tell you how hard/feasible it is to remove or add wires to the existing conduit, but to answer your first question, yes you can feed the shed panel from the basement subpanel.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,258
Location
Modesto, CA
Want to move woodworking power tools from basement to 10x16 foot shed. Shed currently wired in a Connecting Box (not a Panel) via 2" underground #40 PVC to home 200 amp Main Panel with 125 feet of #4 THHN (4 wires including ground). This circuit connects my gasoline generator in the shed to the house when we lose power. Also in the conduit is a 20 amp circuit from the Main Panel to the to the shed for lighting and small power usages (3 wires including ground). I also have a 100 amp sub panel (Sub Panel #1) in the shop area of my basement - about 50 closer to the shed than the Main Panel.

Questions:
1) Is it permissible to feed Sub Panel #2 from existing Sub Panel #1?
2) Using Southwire's Conduit Fill Calculator using the existing Main Panel to shed 2" PVC #40 conduit, 4 wires of the existing #4 THHN wire, and 4 wires of new #6 THHN wire results in a Fill of 15.6% and a Very Low Jam Probability of 6.4%. My question is: Can I remove the existing #10 wire and pull through the new #6 wire without damaging the existing #4 wire? If that is not a wise choice, what are my options?
3) Is it realistic to pull all of the existing cable from the conduit to the shed, remove the #10 wire, and add the #6 wire and then pull the #4 & #6 back through, together?
4) Or, run a new 1" or 1.25" conduit from the Main Panel to the shed for Sub Panel #2 - I could run it side-by-side with the existing 2" conduit. The new Sub Panel #2 will be in a different location than the existing Connection Box in the shed so two conduits would be no problem from a wiring standpoint.

The new Sub Panel will have a 60 amp Main Breaker and grounded with (2) 8 foot grounding rods outside the shed.

Sorry for so many questions but I really want to know what I am talking about before going to my regular electrician.

Many thanks!
Bob

What size feeding breaker do you plan on using for the #2 subpanel? In other words, what size breaker will you be putting in subpanel #1?

1) subpanel #2 is in shed? then yes. you will need to abandoned the current feed...
2) i would not use the southwire calculators. they have errors
3 & 4) i would run a separate conduit.
 