Which type of voltmeter is best for testing fields in a 3 phase motor?

cosmopedro

Well-known member
Joined
Mar 21, 2016
Messages
122
Location
Southwest VT
I have a WEG 5HP 3PH 200V 3440RPM motor I cannot test run because I don’t have 3PH power available, and was hoping to get some feedback on how to test the fields so I can decide whether to buy a VFD and keep it in service on my compressor or buy a single phase motor...

04a13f4144c725b9b86740a888fa2c2d.jpg

I have a digital multimeter and an old analog multimeter, and an electrician co-worker said to measure across the three pairs of wires as indicated in the photo (T1-T6/T2-T4/T3-T5) and should get very low - and even - resistance on each...

Problem is, T1-T6 aren’t both W,U or V... same obviously goes for other two pairs.

Help?


Sent from my iPhone using The Garage Journal mobile app
 

Attachments

  • 04a13f4144c725b9b86740a888fa2c2d.jpg
    04a13f4144c725b9b86740a888fa2c2d.jpg
    40 KB · Views: 0
To avoid these ads, REGISTER NOW!

captaindiode

Well-known member
Joined
Jul 8, 2013
Messages
372
Location
NC
I believe you need to measure between L1 & L2, L2 & L3 , and L1 & L3. I would use the digital on the lowest ohms scale, but the analog will work as well, if you know how to read the scales. Low ohms would indicate the windings are not open. Infinite ohms, a "1" or "OL", on the digital meter would indicate an open winding. Touch the leads on the mter together first and be sure it goes to zero.
 

kschauwe

Active member
Joined
Sep 1, 2012
Messages
32
Location
NW Ohio
2Z1MPWhGzv-w_ZDUy_2pSAXyTEbKnjGS_l_ta2U2nT0mpIalhXimiOhIFa4uHbPAfd0oBSzxK81mHjOJZFZRdgyHeOllp02JEQ8
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,089
Location
Modesto, CA
Testing motor leads with an ohm meter will NOT tell you if the insulation is breaking down which can cause a ground fault when turned on.

Only way to determine this is by energizing the leads.

So the best way to test motor windings is by megging them.

https://forums.mikeholt.com/threads/meggering-a-motor-phase-to-phase.92310/

this is the megger I have which is expensive for one use DIY scenario. There are some cheaper meggers out there though....

https://www.amazon.com/dp/B017OVC2UI/?tag=atomicindus08-20
 
Last edited:
OP
C

cosmopedro

Well-known member
Joined
Mar 21, 2016
Messages
122
Location
Southwest VT
For compressor use, you are almost at parity between buying a correctly sized VFD and replacing the motor with a single phase unit.



I get that, and would prefer to keep original motor/pulley arrangement, but if the original motor isn’t working then my hand is forced... hence the request for assistance on testing it!


Sent from my iPhone using The Garage Journal mobile app
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
11,016
Location
Rhode Island
Just measure across L1-L2, L2-L3, and L1-L3. You should have the same resistance on all three pairs. Then measure L1, L2 and L3 to ground. They should be open circuit.

Not sure what UVW has to do with anything. Those are just labels, just the same as L1, L2, L3.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
That is a 200V motor intended for use on a 208V supply it’s going to be better to buy a proper single phase motor then screw around with a VFD.
 
OP
C

cosmopedro

Well-known member
Joined
Mar 21, 2016
Messages
122
Location
Southwest VT
That is a 200V motor intended for use on a 208V supply it’s going to be better to buy a proper single phase motor then screw around with a VFD.



OK - but isn’t part of the beauty of a VFD is it’s ability to drive these strange (to residential electric) combos, like using single phase 220V to drive 3 phase 200V?

Not challenging anyone, I just thought that was kind of the point...


Sent from my iPhone using The Garage Journal mobile app
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
OK - but isn’t part of the beauty of a VFD is it’s ability to drive these strange (to residential electric) combos, like using single phase 220V to drive 3 phase 200V?

Not challenging anyone, I just thought that was kind of the point...


Sent from my iPhone using The Garage Journal mobile app

220V is a obsolete voltage but if it did exist it would be in the upper range allowed for a 200V motor but a 10 -15 HP VFD would be required because of derating and code requires the circuit for the drive to be sized at 125% of the rated input of the drive, after 3 HP most VFD’s are 3 phase input & some allow the phase loss protection to be disabled & some do not plus at least 50% derate or more is required making the economics doubtful over just buying a new motor.
 
To avoid these ads, REGISTER NOW!

Robbie B

Well-known member
Joined
Jun 24, 2014
Messages
1,320
Location
Sunny side of hell
I have a WEG 5HP 3PH 200V 3440RPM motor I cannot test run because I don’t have 3PH power available, and was hoping to get some feedback on how to test the fields so I can decide whether to buy a VFD and keep it in service on my compressor or buy a single phase motor...

04a13f4144c725b9b86740a888fa2c2d.jpg

I have a digital multimeter and an old analog multimeter, and an electrician co-worker said to measure across the three pairs of wires as indicated in the photo (T1-T6/T2-T4/T3-T5) and should get very low - and even - resistance on each...

Problem is, T1-T6 aren’t both W,U or V... same obviously goes for other two pairs.

Help?


Sent from my iPhone using The Garage Journal mobile app


You want to test t-1 to t-6, t-2 to t-4 and then t3-to t5. Should have some resistance but very low, that tests the individual windings separately. Then test L-1 to L-2, L-1 to L-3, then L-2 to L-3. I’m assuming then W,U and V are the way it’s labeled if the wires are already connected internally but I’m not sure where that is coming from if you have 3 lines coming out of the motor instead of 6 then you’ll just test all three to each other. And as mentioned above this isn’t the best way to test a motor because it can test good here and break down under load. You’d want a megger to test that but most people don’t just have those laying around. And you still have A 200v motor that is a good brand but obsolete. You can just go get a good 5hp, 240v motor at the correct rpm and run it. It’s all depending on how important it is to you to keep it original. I’d just pop a new motor in and roll with it.


Sent from my iPhone using Tapatalk
 

Attachments

  • 04a13f4144c725b9b86740a888fa2c2d.jpg
    04a13f4144c725b9b86740a888fa2c2d.jpg
    37.5 KB · Views: 0

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,089
Location
Modesto, CA

have to derate the drive so that wouldnt work. See norcals comment below

220V is a obsolete voltage but if it did exist it would be in the upper range allowed for a 200V motor but a 10 -15 HP VFD would be required because of derating and code requires the circuit for the drive to be sized at 125% of the rated input of the drive, after 3 HP most VFD’s are 3 phase input & some allow the phase loss protection to be disabled & some do not plus at least 50% derate or more is required making the economics doubtful over just buying a new motor.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
According to the link it is a single phase input drive, still think a new motor is the most economical choice though.
 
OP
C

cosmopedro

Well-known member
Joined
Mar 21, 2016
Messages
122
Location
Southwest VT
I appreciate everyone’s inputs on this, and even though I sourced a 10HP VFD that claimed to be able to run it it seems to me that running a single phase 240V 5HP motor would use less energy than an oversized VFD running a 3-phase motor at the lower limits of the VFD’s output voltage range...

So I’m getting a new motor and H-bushing do I can re-use the old pulley - and while I’m at it I’ll get a frame-conversion plate so it’s still bolt-up. Plus, w/the mounting plate I’ll get the benefit of an adjustment system for belt tension!

Thanks again, everyone! Truly appreciate it!!


Sent from my iPhone using The Garage Journal mobile app
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
11,016
Location
Rhode Island
The efficiency difference would be negligible either way, IMO.

Why are you getting a frame adapter and a pulley bushing? Just buy another 5HP 3500 RPM 184T Frame motor and it will drop right in...
 
OP
C

cosmopedro

Well-known member
Joined
Mar 21, 2016
Messages
122
Location
Southwest VT
The efficiency difference would be negligible either way, IMO.

Why are you getting a frame adapter and a pulley bushing? Just buy another 5HP 3500 RPM 184T Frame motor and it will drop right in...



Because...

https://compressor-source.com/produ...otor-56hz-frame-3440-rpm-single-phase-weg-new @ $219.95

+

https://compressor-source.com/produ...adjustable-slide-plate-universal-56c-mounting @ $19.95

<

https://compressor-source.com/produ...motor-w182-4y-frame-3465-rpm-single-phase-weg @ $299.95

And I get belt tension adjustment to boot.



Sent from my iPhone using The Garage Journal mobile app
 
OP
C

cosmopedro

Well-known member
Joined
Mar 21, 2016
Messages
122
Location
Southwest VT
The efficiency difference would be negligible either way, IMO.

Why are you getting a frame adapter and a pulley bushing? Just buy another 5HP 3500 RPM 184T Frame motor and it will drop right in...



HOWEVER... if y’all know of a 5HP 3500 RPM 184T Frame motor - with a 1-1/8” shaft - for under $259.85 I’m all ears!


Sent from my iPhone using The Garage Journal mobile app
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,339
Location
SE MI
Most DMM do NOT do a good job of measuring small resistances (<10Ω), however you can still use them to COMPARE resistances of each winding. The should all be close.
 