Hey guys a while back I bought a Cornwell plasma cutter for a little body work project on my truck. It worked fine as most of the cuts were pretty short. It's a 16Amp output and you have give it an air supply.
I noticed the other day (this also happened one other time) that if you're cutting thicker metal 1/4 to 3/8 you can only cut about 3-4 inches before it trips the breaker.
Right now I'm in the middle of replacing some wear plates on a skid steer bucket and I'll only cut 2 or 3 inches and let the torch cool. It works, I really need to upgrade to a bigger machine since I've gotten into some bigger jobs.
The circuit in my pole barn it's running off of is 20 amp 12 gauge wire probably about 25-30 feet from the panel.
Should I run a dedicated circuit with 10 gauge wire and use a 10 gauge extension cord?
Not sure why no one else mentioned this but assuming this is the model you have, you are exceeding the rated capacity of the cutter.
Its only designed to cut up to 1/8"
no wonder it trips the breaker.
http://corporate.cornwelltools.com/webcat/products/MMWP125I-%2d-120V-Inverter-Plasma-Cutter.html
cornwell tools said:
Cuts mild steel up to 1/8”...
a 20 amp thermal breaker is only good for 16amps continuous use. that plasma cutter is more than the breaker can handle on thick steels. this is very common on 120v plasma cutters. that machine is likely pulling 18-20 amps during the thicker cuts tripping the breaker. my old blue point is the same way. will cut 100' of 1/8" steel just fine. get up to 1/4" it'll trip a 20amp breaker after 2-3 minutes of continuous cut.
That is completely false. A breaker is good for its rated ampacity.
And the OPs usage is NOT continuous. Do you have a code book handy? Go look up the definition....
you must not work in the electrical industry. We are not talking about "continuous" standby generators. And that continuous is rated for 4 hours or more fyi.
thats a bit ironic when you dont even know the definition of continuous. your own sentence can be thrown right back at you.
Not sure why you brought up standby generators. Has NOTHING to do with this thread.
Continuous is NOT 4hrs.

Since you obviously dont have a codebook I'll quote it for you (FYI you can access it for free online):
NFPA 70/NEC 202; Chapter 1 said:
Continuous Load A load where the maximum current is expected to continue for 3hrs or more.
Continuous is anything more than a momentary start. a 20 amp breaker will start a compressor no problem. a 20 amp will not support a compressor pulling 17-18 amps running load on a 20 amp thermal breaker. It will however run off a 20 amp digital breaker, if you can find one in a residential system.
20 AMP deep fryer is a "continuous load" and will require a 30 amp service to run it.
Wrong again
And motors are a different animal than a plasma cutter. False equivalency.
a 20 amp plasma cutter will not run on a 20 amp circuit cutting max capacity. Period, end of story.
what you failed to see here is that the OP is using the cutter beyond its design limit which is 1/8" mild steel. this is why its tripping.
you should consult your book to see why a 20 amp thermal breaker trips at 16.8 amps on a continuous load. by continuous, I mean more than 10 minutes.
if you can't figure that out, you are not a master anything. a thermal breaker is only rated at 80% of its rating for continuous use.
thanks


you are wrong again.
you should really consult the codebook on what a continuous load is. I posted it above for you in case for whatever reason you couldnt find it yourself.
first you claimed it only applied to standby generators, then you claimed it was more than 4hrs and now you say its more than 10minutes. you've contradicted yourself over and over here. We obviously know who ISNT a master here and its not bert.
Even the breaker manufacturers have white papers that contradict what you say. The egg is on your face.