7.5HP disconnect
bochnak
Mt. Prospect, IL
Looking for an indoor, non fusible, with on/off switch, single phase disconnect.
This will be used to turn compressor on/off when not in garage.
Thanks,
Matt
rlitman
Long Island
930dreamer
Amarillo,TX and Stinnett,TX
Not sure if this is NEC legal, what about a used three phase disconnect and use two of the lines? I see these all the time on FB, CL etc and are usually for larger hp motors.
alfredeneuman
Fullerton, CA
The problem with 3 pole disconnects is they're rated for that HP at 3 phase, not single phase. They aren't labeled or listed for single phase
alfredeneuman
Fullerton, CA
wyliesdiesels
Modesto, CA
That is rated for 2HP. It wont work for the OP
Whats the HP rating on your compressor?
I have this sort of thing for my 5hp (switch made by bryant).
Problem is that going to 7.5hp requires #6 wire and it will be very difficult to stuff in a 4" square box. Assuming they make a version rated for 7.5hp.
You have a snap switch for a 5HP motor? Its probably not rated for the HP youre subjecting it to.
rlitman
Long Island
Good point. You have to read the label. Sometimes they are.
General-Duty disconnects aren't HP rated. Heavy-Duty ones are....and cost more than General-Duty ones.
Is the breaker within sight and not more than 50' away from the equipment?
If so, it would qualify as the disconnecting means
My $12 disconnect has a 15 horsepower rating right on it. From what I've seen, HP ratings are something you need to open the box and look for. It's just not something they print on the outside.
TonyJ
West Virginia
If your running a 7.5 hp compressor then your likely running a magnetic starter also. If so then just put you a switch in line with the coil in the starter and use that to turn it on and off with. And it won’t cost a fortune because the coil runs on very low amps so a small switch can be used
Tony
rlitman
Long Island
Tony
That would be the easiest way to turn the compressor off at night. It doesn't require any HP rating, and makes it potentially simple to mount the switch remotely as well.
tdkkart
Eastern Iowa
Exactly what i did, the controlling switch is one of my light switches by the door, when I leave the shop there's no way for the compressor to run.
exranger06
CT
I also recommend switching the coil of the starter. That's what I did on mine. I have a remote toggle switch to turn it on and off from the garage. The compressor is in the basement on the other side of the house.
rlitman
Long Island
Well, I won't say there's anything wrong with this approach, but I don't actually ever shut my compressor off (though a shutoff to the starter is on my to-do list). I have a motorized ball valve at my tank that I shut off remotely. When it's off there are no leaks whatsoever, so it can sit for weeks without cycling, and it doesn't immediately run when I turn it on.
Had I only shut down the power, it would have to pump all the way back up each time I use it.
Ilikeike
Northern Ca.
I have a knife switch type disconnect on my little compressor shed outside my garage, but since I'm quarantined bored right now, and thinking of garage stuff to do, I was thinking about a remote mounted E-Stop mounted in my garage by the door into the house so I wouldn't forget to kill it, then just run to a contactor out by the compressor before the service disconnect.
Hmmm:headscrat
bochnak
Mt. Prospect, IL
Here is a toggle switch with 60A / 20hp rating. Question is what do you house it in with enough room for wires?
https://www.automationdirect.com/ad...ntrollers_-z-_disconnects_(30-60_amps)/60002d
exranger06
CT
I don't really HAVE to shut mine off. My system is pretty much leak free. I leave all of the piping and hoses fully pressurized 24/7. If I left the switch turned on 24/7, the compressor would probably only turn on once a month (that is, if I don't actually use it). But I like to turn the power off just in case a leak ever springs up.
Lightning rod
Toronto , Ontario
Since i retired last year i find that my brains are slowly turning to mush to the extend that i don’t always fully explain what my recommendations are based on.
You guys are correct in that the proposed switch is not rated to switch “in and out” a 7.5 HP compressor.
I assumed that the compressor already had a magnetic starter on it and the OP Was looking for a way to make sure that the power was off to the compressor when he wasn’t around.
The proposed switch will not be used to switch the compressor directly
Only when the compressor is not running.
Thats what i did in my garage.