This is my panel in my garage. Fed from my house panel with 2224 .no power to it yet, but looking for input.
 

Attachments

  • 20200701_173748.jpg
    20200701_173748.jpg
    97.2 KB · Views: 275
To avoid these ads, REGISTER NOW!

Copymutt

Well-known member
Joined
Sep 3, 2016
Messages
3,392
Location
Colorado
Only comment I have.
Are the feeds aluminum?
If so coat the ties w/ an oxidation preventer.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,582
Location
Fullerton, CA
You need to have an insulating bushing on the PVC Male Adapter.
It's required for any wire #4 and larger. (If it's like that at the panel on the house you'd need one there too)
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,764
Those panels are made to be flipped for bottom feed, which keeps things a lot cleaner by not having a bunch of excess conductor in the panel gutter, it’s not “upside down” if you had done it that way. And as already mentioned the PVC terminal adapters need bushings.
 

Lassen Forge

Well-known member
Joined
Apr 26, 2014
Messages
15,277
Location
The romantic hills of central Umbria, Italy,
I agree with ^^^ on the installation issues...

Functionally, , I have Zinsco panels (I know, e-w-w-w) with aluminum busses, and I both make sure they're coated AND pull them down annually to inspect. Not a big deal for me, but eventually I want to go with something better, newer, and safer.

The only other issue I'd have is ampacity... I have 100 amo service on mine as well, but a few 220 consumers on mine, so I notice the hit when something kicks on.
 

spudley

Well-known member
Joined
Dec 27, 2016
Messages
702
Location
Northeast Wisconsin
Those panels are made to be flipped for bottom feed, which keeps things a lot cleaner by not having a bunch of excess conductor in the panel gutter, it’s not “upside down” if you had done it that way. And as already mentioned the PVC terminal adapters need bushings.
Aside from the "excess" of running the conductors from the bottom to top, is it permissible to route this way?
 

Jakemedic

Well-known member
Joined
Jul 26, 2013
Messages
722
Location
Cornfields of SE Iowa
Remember to tighten the lugs appropriately, oxidation prevention and the pvc bushing adapter. I turned my box upside down to minimize hot feeds in. Looks good otherwise!
 
Last edited:
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,031
Location
Modesto, CA
This is my panel in my garage. Fed from my house panel with 2224 .no power to it yet, but looking for input.

If this is a detached structure then youre missing the GEC which would go to 2 grounding electrodes.

Only comment I have.
Are the feeds aluminum?
If so coat the ties w/ an oxidation preventer.

not necessary and not required by code unless manu. requires it.

What's the yellow coming out of the conduit?

looks like poly rope. good way to burn a hole in sweeps...
 
OP
R

Ron_J

Well-known member
Joined
Jul 10, 2018
Messages
295
Location
Central PA
I'm pretty certain it is a wire pulling string.

Correct, that is my pulling string.

As for the terminal adapter? I'm not sure what you mean...I have an offset adapter on it already.

like this... https://www.lowes.com/pd/CARLON-2-i...VhorICh3gCQTzEAQYAiABEgI5ivD_BwE&gclsrc=aw.ds
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,031
Location
Modesto, CA
Correct, that is my pulling string.

As for the terminal adapter? I'm not sure what you mean...I have an offset adapter on it already.

like this... https://www.lowes.com/pd/CARLON-2-i...VhorICh3gCQTzEAQYAiABEgI5ivD_BwE&gclsrc=aw.ds

the terminal adapter is the PVC coupling with threads on one side used to connect the conduit to the panel

you need a plastic insulating bushing on it

https://www.homedepot.com/p/Halex-2-in-Rigid-Plastic-Insulated-Bushing-4-Pack-27526/100169597
 

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,828
Location
Southern Oregon
Next time put a ground bar on the other side of the panel too. Keeps from having to route the grounds across. That gets harder to do as you add more more circuits and have to weave your way through them.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,764
Aside from the "excess" of running the conductors from the bottom to top, is it permissible to route this way?

It is permitted. Puppies and kittens will still be born blind no matter what way it’s done . :D
 