Outside Sub-panel for AC units

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
I have three AC compressors going into the same spot. Does it not make sense to have a small sub-panel vs all these wires and boxes?

was going to talk about running one feeder wire to the panel and then whips out to each unit ....have the courtesy outlet from the panel. I could use it for my outside tree light feed as well.

was thinking it could be on a wood post (Maybe metal is code?) .. can't the panel be the disconnect for the AC units this way?
 
Last edited:
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,587
Location
Fullerton, CA
Does it not make sense to have a small sub-panel vs all these wires and boxes?
.. can't the panel be the disconnect for the AC units this way?

Yes it makes perfect sense.
If the nameplates on the units give a Max Fuse or Circuit Breaker size you can use the breakers in the panel as disconnects.
If it says only Max Fuse size you can't
 
OP
Y

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
Yes it makes perfect sense.
If the nameplates on the units give a Max Fuse or Circuit Breaker size you can use the breakers in the panel as disconnects.
If it says only Max Fuse size you can't

That's interesting .... Why not ? What's the significance/ distinction?

It's a residential Carrier Condenser and two Mitsubishi Mini-split condensers.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,054
Location
Modesto, CA
That's interesting .... Why not ? What's the significance/ distinction?

It's a residential Carrier Condenser and two Mitsubishi Mini-split condensers.

Because if it says Fuse only, then you will need a fusible disconnect in addition to the breakers in the subpanel.

Some types of fuses react differently to overloads and short circuits than breakers do and some condensers require fuses only. Check the nameplate.
 

snorky18

Well-known member
Joined
Oct 1, 2007
Messages
1,170
Location
Southeast Tennessee
I've considered the same.

The main thing I haven't looked into... I believe with a dedicated HVAC circuit the OCPD can be higher ampacity than a given conductor would typically allow. So would my subpanel then need to be fed with the size conductor to support that higher OCPD continuously?
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,886
I'd do external panel sized for all 3, then your standard AC disconnects at each unit location. at the fuse disconnect you can transfer over to liquid tight. it'll look real clean.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,587
Location
Fullerton, CA
The 3 are going "in the same spot" according to yeldogt (right next to one another).
The sealtite whips can come right out of the panel if it meets the nameplate breaker requirement, which would look even cleaner
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,054
Location
Modesto, CA
I'd do external panel sized for all 3, then your standard AC disconnects at each unit location. at the fuse disconnect you can transfer over to liquid tight. it'll look real clean.

why bother with individual disconnects? just adds unneeded complexity when the breaker is right there....
 
OP
Y

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
The two mini split compressors will be end to end (9k and 18k) with the Carrier sitting behind them ... So they are all together. Having the whips direct to the units would be ideal.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Unless my memory fails me, but won't all the units need to be within 6ft of the sub panel to meet the 6ft limit of LFNC?
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,764
Location
NW Iowa
Unless my memory fails me, but won't all the units need to be within 6ft of the sub panel to meet the 6ft limit of LFNC?

Where do people get this stuff?

It's only limited to six foot when unsupported. You can run it as far as you want if you put some straps on it.
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Where do people get this stuff?

The only time seal tight would be limited to 6' would be if you are using it for the ground. If you pull a ground you can run the stuff as far as you want.

I get it from NEC 356.12(3) LFNC, you're thinking of FMC used for grounding.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
A subpanel would also be convenient for adding the code required service receptacle within 25 feet of the units, if you don't already have one.
 
To avoid these ads, REGISTER NOW!

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,023
Location
Coronado, CA
Please correct me if I am wrong, as long as the disconnects are within sight of the AC Units and within wrench throwing distance, IMHO an exterior sub panel would be OK.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Ok so put a ******** it.

I was just commenting about want I recalled about LFNC. The a/c whips at the big box stores are normally 6' LFNC, so that's what made me think about it.
I just didn't appreciate your comment starting off with an insult.
 
OP
Y

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
What type of wire has to come out of the wall ?

I'm doing this because the property is very tight on mechanical space -- and it's a stone building. I want the units a few feet from the building and I don't want boxes in the building.

I'm thinking a conduit to the sub on some type of post ... the whips to the units. We are going to design a screen to obscure the units.

Can you run some type of wire through the house and keep this same wire in the conduit to the sub?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,767
Any conduit outdoors or underground is a wet location so the wire must be rated for wet location use like THWN.
 
OP
Y

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
Any conduit outdoors or underground is a wet location so the wire must be rated for wet location use like THWN.

But -- How do you do that all the way back to the panel of you can't run conduit all the way back to the panel ?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,767
Going to have to transition from NM cable to a wiring method suitable for a wet location.
 
OP
Y

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
Or use uf all the way. But let's calculate the wire size.


This is not DIY ..... I'm thinking.

I went the the property Wednesday as they were prepping the spot for the units with a backhoe .... was also looking at the very limited space for wires. The panel and most of the mechanicals are housed in the new addition and the wires have to go through the old stone building. Getting through 2' of stone wall is not easy and we only have so many points through.

My guess is where the panel would be ideal is 3' ..maybe 4' from the wall of the old stone building.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I would likely be done before I could get someone else involved. Some part might be hard, duh, that's why they don't get old women and children to do it.
 
OP
Y

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
I would likely be done before I could get someone else involved. Some part might be hard, duh, that's why they don't get old women and children to do it.

Don't follow ...sorry.

My builder was on it -- I'm glad my generator is a 22k -- as the 3T is not going to pose a problem. Was planning on using a load control on the 3T ..

May need to control the shop.
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,833
Location
Austin, TX
I'm adding Siemens Talon (subpanels with 50A, 30A, 20A GFCI outlets) to HVAC compressor installs.. It's just a flexibility thing for me. The panel breakers serve as readily accessible disconnects and because the panel has 20A, it meets that requirement also.
 
OP
Y

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
I'm adding Siemens Talon (subpanels with 50A, 30A, 20A GFCI outlets) to HVAC compressor installs.. It's just a flexibility thing for me. The panel breakers serve as readily accessible disconnects and because the panel has 20A, it meets that requirement also.



That's the way it's going ... they are at the house now. The builder put in a temp post and sparky is going to run the wire from the main and mount a box.

We need to get some of the AC working so the inside can be conditioned for the stairs and other millwork.

He many just use a temp box and loop some extra wire -- we only need to get the one going. When the AC guys are ready to set the other units we will have a better idea of the proper placement. Sparky mentioned we need 3' ... so that may change location.

Naturally, this is a very space challenged project ... And I need to hide 4 compressors. It always works that way!
 
Last edited: