Getting 220v 50amp out to the garage

colt.45

Member
Joined
Aug 31, 2009
Messages
15
here is the thing i just got my first tig welder. and now i feel like a little with a new toy and no batteries for it. so im looking at my options to get a the power out to the garage, already have 120v run out to the garage for a couple outlets and lights, so i have a path and all that.

but, right now we have a 100amp service in the house. with an unused 220v 20amp fuse that use to go to an attic fan, that doesnt work. around sept we are gonna upgrade the house to 200 amp service and work out a better power plan to the garage,

i would rather not wait that long to use the welder though,

so could i use that open 220v and run it to the garage for a 50 amp plug, i know a couple of electricians, and they would help me out when we do it, but for right now im wondering if its doable in that way, or is it a major violation of code and safety and all that stuff.
 
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
is the garage detached? if so, you cant do it -only one circuit is allowed to a detached structure.
 
OP
C

colt.45

Member
Joined
Aug 31, 2009
Messages
15
no the garage is attached. and as far as 1 circuit to detached, that why people put 60a or 100a boxes in there garage?
 

rodm1

Well-known member
Joined
Feb 17, 2008
Messages
2,270
It's doable but you will have to run new wire for the 50amp. You should run 100amp cable or better if you are upgrading cheaper now. I would rate everything for 200amp's if it whose me.
 
Last edited:
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
no the garage is attached. and as far as 1 circuit to detached, that why people put 60a or 100a boxes in there garage?

yes, among other reasons.

I reread your post and it said 220v fuse. Is your panel fuses or circuit breakers?
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
sorry my mistake, the box uses circuit breakers.


ok, so yeah (ignoring potential load issues (dont run the electric oven or electric heat when youre welding)) replace the 2P 20A with a 2P 50A breaker, run some 6/2 romex over to a NEMA 6-50 receptacle and call it a day.
 