GFCI Breaker popping

akpolaris

Well-known member
Joined
Jun 14, 2010
Messages
214
Location
Seward, Ak
I have a circuit for my residential exterior lighting that is GFCI protected. All the boxes are inside and not exposed to weather. 3 exterior lights on the residence with boxes inside the t1-11 siding. 3 unheated outbuildings with a couple of exterior lights and interior lights in each. Switches are inside the sheds. Recently the GFCI in the house popped and I replaced it assuming that it was just failing, aged. now the new breaker is popping quite intermittently and a few days later it will function fine again. I have checked the boxes and the connections seem secure. After talking with an electrician he suggested that the boxes may be getting condensation which is melting / dripping in the box. He suggested using duct seal on the face of the boxes and replacing the plates. Sound idea?? The entire box is in unheated spaces so I am not sure how sealing the faceplate is a solution. This circuit has been functioning with no problem for 8 or 10 years until recently. I haven't tracked the failures against the changing weather. I am in a temperate part of Alaska so we do have some temps that fluctuate and plenty of rain and snow.
 
To avoid these ads, REGISTER NOW!

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,105
Location
VT
The GFCI feeds a circuit that goes to 3 outbuildings?

Is this wire underground or exposed?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,031
Location
Modesto, CA
I have a circuit for my residential exterior lighting that is GFCI protected. All the boxes are inside and not exposed to weather. 3 exterior lights on the residence with boxes inside the t1-11 siding. 3 unheated outbuildings with a couple of exterior lights and interior lights in each. Switches are inside the sheds. Recently the GFCI in the house popped and I replaced it assuming that it was just failing, aged. now the new breaker is popping quite intermittently and a few days later it will function fine again. I have checked the boxes and the connections seem secure. After talking with an electrician he suggested that the boxes may be getting condensation which is melting / dripping in the box. He suggested using duct seal on the face of the boxes and replacing the plates. Sound idea?? The entire box is in unheated spaces so I am not sure how sealing the faceplate is a solution. This circuit has been functioning with no problem for 8 or 10 years until recently. I haven't tracked the failures against the changing weather. I am in a temperate part of Alaska so we do have some temps that fluctuate and plenty of rain and snow.

wow you have a lot on this one circuit. might be difficult to track it down

can you disconnect some of the outbuildings to isolate part of the circuit and see if it still trips?

A GFCI wont trip due to moisture simply being inside the box. The moisture would need to make a connection between hot and ground or neutral and ground creating a current imbalance on the hot and neutral...

also, a loose connection will not cause a GFCI or standard breaker to trip. Only an AFCI breaker would trip with a loose connection, because of the associated arcing.
 

510ebl

Well-known member
Joined
Jan 20, 2015
Messages
518
Location
Southern New Jersey
Is the breaker actually tripping or is the GFI going into “fault”?

Is there a single junction box where all these circuits are being distributed, or do they “Daisey chain” along?
 

mcspeed

Well-known member
Joined
Jul 13, 2017
Messages
82
If there are any extension cords or connections exposed to rain they could be the issue. I see it all the time.

These work pretty well.
IMG_0895.jpg


Sent from my iPhone using Tapatalk
 
OP
A

akpolaris

Well-known member
Joined
Jun 14, 2010
Messages
214
Location
Seward, Ak
The wire does go underground between the buildings. It is bury able wire. It is surface mounted 12-2 wire except for 1 light switch which is a 2 way switch

UOTE=PCustoms;8808418]The GFCI feeds a circuit that goes to 3 outbuildings?

Is this wire underground or exposed?[/QUOTE]
 
OP
A

akpolaris

Well-known member
Joined
Jun 14, 2010
Messages
214
Location
Seward, Ak
I may have put in an AFCI but don't think so. I'm a bit confused by the applications and their use. The odd part is that this just recently started and I don't know what triggers it. Everything worked fine for years which led me to believe it was a faulty breaker. It will trip and not hold for 2 or 3 days then function fine. I guess the isolating of each building or component is a start next time it fails.
If the condensation liquified it could drip on a wire? but nothing is exposed, it is captured in wire nuts. Except the screws to the switches and fixtures

wow you have a lot on this one circuit. might be difficult to track it down

can you disconnect some of the outbuildings to isolate part of the circuit and see if it still trips?

A GFCI wont trip due to moisture simply being inside the box. The moisture would need to make a connection between hot and ground or neutral and ground creating a current imbalance on the hot and neutral...

also, a loose connection will not cause a GFCI or standard breaker to trip. Only an AFCI breaker would trip with a loose connection, because of the associated arcing.
 
OP
A

akpolaris

Well-known member
Joined
Jun 14, 2010
Messages
214
Location
Seward, Ak
At the 1st building there is a 3 way switched lite fixture, with a switch in the house and out at the lights. Then the power "daisey chains" or goes "in series" from there
Is the breaker actually tripping or is the GFI going into “fault”?

Is there a single junction box where all these circuits are being distributed, or do they “Daisey chain” along?
 
To avoid these ads, REGISTER NOW!
OP
A

akpolaris

Well-known member
Joined
Jun 14, 2010
Messages
214
Location
Seward, Ak
What is the difference between "tripping" & "fault"?

Is the breaker actually tripping or is the GFI going into “fault”?

Is there a single junction box where all these circuits are being distributed, or do they “Daisey chain” along?
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,982
Location
Coronado, CA
I once had a similar problem with a post lamp fed by an underground cable. 25 years ago I installed an isolation transformer, the problem has not reoccurred.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,031
Location
Modesto, CA
What is the difference between "tripping" & "fault"?

A GFCI breaker has 3 "trip" components whereas a regular breaker has 2

GFCI breaker:
  1. thermal for overloads above a certain percentage of breaker rating
  2. magnetic for line to line short circuit faults
  3. ground fault for current imbalance between hot & neutral

a regular breaker only has 1 and 2.

so the GFCI breaker could be tripping due to a ground fault or overload trip

I doubt its an overload though...

the underground cable could have a bad spot in the insulation from a rock. when it gets wet, it causes a line to neutral or line to ground fault, which causes the GFCI portion of the breaker to fault

What brand and model of breaker do you have? some have an indicator that tells you why it tripped. Also, when it faults, you could take a multimeter (with breaker still off) and measure resistance between the hot lug on the breaker and the circuit neutral and then between hot and ground to see if you get continuity.
 
OP
A

akpolaris

Well-known member
Joined
Jun 14, 2010
Messages
214
Location
Seward, Ak
I am away from home, work remotely. I believe it is a Siemens. This seems to fault or trip when I am out of town. Can't be my wifes' fault??? LOL

A GFCI breaker has 3 "trip" components whereas a regular breaker has 2

GFCI breaker:
  1. thermal for overloads above a certain percentage of breaker rating
  2. magnetic for line to line short circuit faults
  3. ground fault for current imbalance between hot & neutral

a regular breaker only has 1 and 2.

so the GFCI breaker could be tripping due to a ground fault or overload trip

I doubt its an overload though...

the underground cable could have a bad spot in the insulation from a rock. when it gets wet, it causes a line to neutral or line to ground fault, which causes the GFCI portion of the breaker to fault

What brand and model of breaker do you have? some have an indicator that tells you why it tripped. Also, when it faults, you could take a multimeter (with breaker still off) and measure resistance between the hot lug on the breaker and the circuit neutral and then between hot and ground to see if you get continuity.
 
OP
A

akpolaris

Well-known member
Joined
Jun 14, 2010
Messages
214
Location
Seward, Ak
So can I test this breaker in this manner by just switching it off or does the testing need to be done when it is "tripped"?

A GFCI breaker has 3 "trip" components whereas a regular breaker has 2

GFCI breaker:
  1. thermal for overloads above a certain percentage of breaker rating
  2. magnetic for line to line short circuit faults
  3. ground fault for current imbalance between hot & neutral

a regular breaker only has 1 and 2.

so the GFCI breaker could be tripping due to a ground fault or overload trip

I doubt its an overload though...

the underground cable could have a bad spot in the insulation from a rock. when it gets wet, it causes a line to neutral or line to ground fault, which causes the GFCI portion of the breaker to fault

What brand and model of breaker do you have? some have an indicator that tells you why it tripped. Also, when it faults, you could take a multimeter (with breaker still off) and measure resistance between the hot lug on the breaker and the circuit neutral and then between hot and ground to see if you get continuity.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,031
Location
Modesto, CA
So can I test this breaker in this manner by just switching it off or does the testing need to be done when it is "tripped"?

you can test it with it off or tripped. doesn't matter.

but if you test it right after its tripped, it may give you a better idea of what the problem could be.
 

torqueman2002

Well-known member
Joined
Jun 3, 2009
Messages
6,141
Location
SE Michigan
I have a lamp post with an outlet that are connected to an inside GFCI.

It has been fine for years.

About 4 months ago, I installed a new lamp fixture and LED lamp. They worked well throughout the summer, but when the fall/damp weather came along, the GFCI began tripping.

I replaced the GFCI thinking it may be faulty, but the new one continued to trip.

After replacing the LED lamp with an incandescent one, the GFCI has not tripped.
 