Second Ground Source Recommendation
DrtroitMuscle
I had a subpanel professionally installed in my basement for the purposes of a future remodel some time ago. It is directly adjacent to the main. There is a ~ 1ft long second ground wire that connects the metal of the sub to the metal of the main. See upper right of pic.
I'm considering adding a sub in the ATTACHED garage for workshop tool circuits. The sub will be located about 60' from the main and will be a challenge to fish the wire alone (not planning to use conduit except for the very final stretch to surface mount the panel). Is there a typical method for getting the second ground? Should I run a separate ground wire from the main (not sure that is even really possible unless I use conduit)? Or would it be easier to use a ground rod since the sub won't be that far from an external wall?
Advice is much appreciated.
D
DrtroitMuscle
I plan on using 4 conductor wire (6/3 romex to be specific). But the basement panel has a 5th wire that joins the conduit section that touches the sub to the conduit section that touches the main. Seems to me a I need to do the same for the garage sub or use a ground rod. No? Overkill?
wyliesdiesels
Modesto, CA
That ground wire is a conduit bond and is not necessary. the conduit is metal end to end and is bonded to the main and the sub.
you only need 4-wires for a subpanel- 2 ungrounded/hot conductors, 1 grounded/neutral conductor, and 1 ground/equipment grounding conductor.
Make sure the neutral bar(s) is unbonded in both subpanels.
A ground rod/grounding electrode is not the same thing as an EGC or bond wire.
D
DrtroitMuscle
Thank you so much wyliesdiesels. I did some more googling and I better understand the setup now. I really appreciate your comments!
greg13
Weedsport, NY
I think code requires TWO ground rods no closer than 6', at least that is what I did in my garage.