39CAMC
Well-known member
Summary/TL;DR: Its obviously a floating or bonded ground issues, my question is How do I fix it?
We have an enclosed trailer we use to sell my companies products out of. I has 110V wiring in it with an reverse plug on the front of the trailer.
At the shop, we power it from a regular extension cord. At events, we use either a Honda EU2000 inverter generator or a Champion 10029 3400W Inverter generator.
It has worked fine for several years.
We upgraded a piece of equipment and need 220V so I picked up a Briggs Q6500 inverter generator which works great for the 220V equipment but when I hook the 110v outlet to the trailer, the GFCI outlet on the generator trips immediately.
This generator has a Bonded Ground(I think?) (below from the manual)
>>>>>>>>>>>>>>>>>>>>
System Ground
The generator has a system ground that connects the generator
frame components to the ground terminals on the AC output
receptacles. The system ground is connected to the AC neutral
wire (the neutral is bonded to the generator frame).
>>>>>>>>>>>>>>>>>>>>>
I am not sure on the ground type on the other generators, but they also do not have GFCI outlets.
So, as noted above, it is presumably an issue with a bonded versus floating ground.
But I guess I do not know where to start to fix the problem.
Do I need to change the wiring in the trailer? It has an RV type breaker box in it. Or will one of those plugs like this work?
https://inverterservicecenter.com/s...qU6A-SRa8M04GJov7mbi70hThSqccKlIaAgFlEALw_wcB
Thanks in advance for any help,
DaveW
We have an enclosed trailer we use to sell my companies products out of. I has 110V wiring in it with an reverse plug on the front of the trailer.
At the shop, we power it from a regular extension cord. At events, we use either a Honda EU2000 inverter generator or a Champion 10029 3400W Inverter generator.
It has worked fine for several years.
We upgraded a piece of equipment and need 220V so I picked up a Briggs Q6500 inverter generator which works great for the 220V equipment but when I hook the 110v outlet to the trailer, the GFCI outlet on the generator trips immediately.
This generator has a Bonded Ground(I think?) (below from the manual)
>>>>>>>>>>>>>>>>>>>>
System Ground
The generator has a system ground that connects the generator
frame components to the ground terminals on the AC output
receptacles. The system ground is connected to the AC neutral
wire (the neutral is bonded to the generator frame).
>>>>>>>>>>>>>>>>>>>>>
I am not sure on the ground type on the other generators, but they also do not have GFCI outlets.
So, as noted above, it is presumably an issue with a bonded versus floating ground.
But I guess I do not know where to start to fix the problem.
Do I need to change the wiring in the trailer? It has an RV type breaker box in it. Or will one of those plugs like this work?
https://inverterservicecenter.com/s...qU6A-SRa8M04GJov7mbi70hThSqccKlIaAgFlEALw_wcB
Thanks in advance for any help,
DaveW