Quick wiring question

earlybirds

Well-known member
Joined
Feb 12, 2010
Messages
70
Location
eastern Iowa
I will be adding 2 rows of lighting in my detached shop. Each row will have its own switch. These 2 rows will be powered from a single 15 amp breaker in the subpanel.14 gauge THHN wiring in EMT conduit. Can these 2 rows share a neutral wire back to the subpanel, or does each row need its own neutral wire back to the subpanel?
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,794
I will be adding 2 rows of lighting in my detached shop. Each row will have its own switch. These 2 rows will be powered from a single 15 amp breaker in the subpanel.14 gauge THHN wiring in EMT conduit. Can these 2 rows share a neutral wire back to the subpanel, or does each row need its own neutral wire back to the subpanel?

Only one is required. If it was two different circuits on the same leg then two would be required, but if it were two circuits on different legs of the panel then only one would be required. Your good to go with only one, any more would be wasting wire.
 

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,942
Location
Central New Jersey
Make sure to run the neutral to both switch boxes as well.

Neutrals are now required by code per the NEC to be in switch boxes, presumably so that if you change a regular switch to a fancier WIFI, smart switch or one that requires a neutral, you will be able to do that.

Jim
 

grounded-b

Well-known member
Joined
Oct 23, 2012
Messages
285
Location
Milwaukee, WI
Make sure to run the neutral to both switch boxes as well.

Neutrals are now required by code per the NEC to be in switch boxes, presumably so that if you change a regular switch to a fancier WIFI, smart switch or one that requires a neutral, you will be able to do that.

Not required by the NEC if wiring method is conduit to the switch.

If needed at a later date, a grounded conductor can be pulled through the conduit.

Steve
 
To avoid these ads, REGISTER NOW!

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,942
Location
Central New Jersey
Not required by the NEC if wiring method is conduit to the switch.

If needed at a later date, a grounded conductor can be pulled through the conduit.

Steve

I thought that was only true for homes/wiring installed before 2011 where the conduit is already in place due to the use of switch loops where the white wire is designated as a switched hot? But he might as well do it now since this is an all new setup.

Jim
 
Last edited:

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,794
I thought that was only true for homes/wiring installed before 2011 where the conduit is already in place. But he might as well do it now if this is an all new setup.

Jim

He is correct about not being required if in conduit. If the wiring method were NM or MC cable then it would be required.
 

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,942
Location
Central New Jersey
He is correct about not being required if in conduit. If the wiring method were NM or MC cable then it would be required.

Ok, gotcha! I thought it was required after the NEC said no more 2 wire switch loops, where a white wire could be designated as a switched hot.

But that would fall under the use of NM cable I would guess.

Jim
 