andyvh1959
Well-known member
See the attached picture of my 1973 CH Load Center. Some time back someone installed Central Air, and the wires from the Load Center to the AC box exit the panel at the bottom right and go through the garage wall. I feel I need to rewire that for a couple reasons:
1. The wire is a 10/2-G, so the black AND the white both go to the 30amp duplex breaker, but the white wire is not re-colored red.
2. There is no neutral from the AC box to the neutral bus bar. Only a a ground wire to the ground bus bar.
3. The 10/2 wire is not properly stapled to the wall stud.
I assume an electrical inspector would make me correct these issues even though I never did them to begin with. The inspector is coming later this month to review and approve my new sub panel connection of this load center.
Oh, odd thing too. The Cutler Hammer panel has enough slots on the door for an additional six breakers. But, there is only enough power bus to allow for three additional breakers. Seems odd that the power bus is not long enough to allow for the additional breaker spaces. I also found two breakers in the panel, each with two blacks coming from the breaker. On one of them, a black wire is not sufficiently tight under the screw. There is one unused 15 amp breaker, so I'll wire a circuit to that. I can also add one more single breaker, in addition to the 100 amp duplex breaker going in for the sub panel, so I can add another 15 amp breaker. Then all the circuits in this messy looking panel will be wired to individual breakers.
1. The wire is a 10/2-G, so the black AND the white both go to the 30amp duplex breaker, but the white wire is not re-colored red.
2. There is no neutral from the AC box to the neutral bus bar. Only a a ground wire to the ground bus bar.
3. The 10/2 wire is not properly stapled to the wall stud.
I assume an electrical inspector would make me correct these issues even though I never did them to begin with. The inspector is coming later this month to review and approve my new sub panel connection of this load center.
Oh, odd thing too. The Cutler Hammer panel has enough slots on the door for an additional six breakers. But, there is only enough power bus to allow for three additional breakers. Seems odd that the power bus is not long enough to allow for the additional breaker spaces. I also found two breakers in the panel, each with two blacks coming from the breaker. On one of them, a black wire is not sufficiently tight under the screw. There is one unused 15 amp breaker, so I'll wire a circuit to that. I can also add one more single breaker, in addition to the 100 amp duplex breaker going in for the sub panel, so I can add another 15 amp breaker. Then all the circuits in this messy looking panel will be wired to individual breakers.