I'm wiring my barn with EMT and metallic boxes. Instead of the typical steel boxes, I'm using the outdoor aluminum boxes since they are fully sealed for dust ingress (horse barn). I typically won't run a ground with steel boxes and just ground to the conduit. Can I do the same with the aluminum boxes. Box selection is very limited in these as is space. The box in the attachment is one of the ones I'm using. It's 18cu in. If I run an outlet, two 12Ga conductors that pass through for a second light circuit and the four 12Ga wires that terminate on the outlet, I'm at the limit for 18cu in. If I run a separate ground conductor I'll go over. What's the normal consensus for these aluminum boxes? Are they appropriate without a separate ground conductor? I'll be using steel compression fittings with the EMT.