Has any one use rolls of fiberglass insulation in a metal building garage and if so how did it work out thanks
 
To avoid these ads, REGISTER NOW!

readhead

Well-known member
Joined
Dec 8, 2012
Messages
6,187
Location
Durango, Co.
What type of metal building? Was there a thermal break tape installed between the cover and the frame? Will there be an inside wall covering? Will you be heating or cooling or both? Where are you located? It would be helpful if that was in your profile. This info will have a bearing on what path you take for insulation.
 
OP
D

Dubbydoo

Well-known member
Joined
Jan 22, 2011
Messages
275
Sorry in in VA gets hot and humid here in the summer and pretty cold in winter. I will be cooling and heating. there is nothing on the walls just metal on metal frame. If i use the roll insulation I was gonna skin the inside walls with exterior metal panels like the same same that used on the outside
 

Gunfixr

Well-known member
Joined
Feb 9, 2021
Messages
677
Location
behind the house
I'm in VA, and I have a metal building also. Humidity gets in mine pretty bad. Using roll up insulation isn't going to keep that out. The brother of a friend who has one sprayed in insulation, sealed it right up.
 

readhead

Well-known member
Joined
Dec 8, 2012
Messages
6,187
Location
Durango, Co.
I’m guessing it is a tube steel building and it is metal on a metal frame. Since there is no thermal break condensation is still in the cards. Was a vapor barrier installed under the slab?
my suggestion would be to use 2” rigid foam flush to the inside of the frame So there is a small gap between the foam sheets and the siding. Use a 3/8” thick foam tape on the face of the frame before you install the interior sheeting.
As a side note to others reading this it is always less expensive and easier to insulate during construction than afterwards. If the budget doesn’t allow during construction you should at least install a thermal break between the siding and the frame to reduce condensation.
 

My Old Tools

Well-known member
Joined
Jun 4, 2014
Messages
5,450
Location
Hamrick Lake, TX
Its humid as hell here. My building is red iron, 30x40s12 with 6/12 roof. 22 feer tall. Its insulated with plastic faced fiberglass roll, but was installed before the sheets. I added another 8 inch layer on the roof only. It stays nice and cool in summer and warm in winter with a 3 ton MrCool. Probably could have done a 2 ton.
 

That Guy Scott

Well-known member
Joined
Dec 31, 2010
Messages
141
Location
SoCal
I’m guessing it is a tube steel building and it is metal on a metal frame. Since there is no thermal break condensation is still in the cards. Was a vapor barrier installed under the slab?
my suggestion would be to use 2” rigid foam flush to the inside of the frame So there is a small gap between the foam sheets and the siding. Use a 3/8” thick foam tape on the face of the frame before you install the interior sheeting.
As a side note to others reading this it is always less expensive and easier to insulate during construction than afterwards. If the budget doesn’t allow during construction you should at least install a thermal break between the siding and the frame to reduce condensation.
What if it’s a red iron style with no thermal break? What is your thoughts there? I failed to do what you recommended above and Im now contemplating doing some insulation. I know you’re not a fan of spray insulation.
 

misterfixit

Well-known member
Joined
Feb 9, 2013
Messages
199
Location
Kaufman Texas
Maybe not what you want to hear, but my own metal frame metal siding 30x40x12 was sprayed with closed cell foam. seals great and while not the cheapest method it is probably the fastest and easiest after construction is completed.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,727
Location
Fargo, ND
You can insulate it with about anything, but make sure you get the sill and any seams sealed up.

I was on a construction job a few years back. We did hydronic floor heat in a steel building that was an unheated storage barn. Another contractor insulated and finished the walls. They could barely heat the place. One windy day I went back to figure out the problem. I walked into the building and I could feel the air moving. I grabbed a piece of toilet paper and walked around the walls. Any opening, electrical outlet, any seam in the wall board and it would blow the toilet paper away.

They got the contractor back and showed him the issue. They stripped all the wall board off and spray foamed the walls and ceiling and refinished the interior. Basically did the whole job over. It heated fine after that.
 

readhead

Well-known member
Joined
Dec 8, 2012
Messages
6,187
Location
Durango, Co.
Scott, there are retro fit systems that use fiberglass blanket insulation. Try Silvercote.

I need to make my position clear again on spray foam. I think it is a great product that does exactly what it promises. I would use it in my house if I had the opportunity. Over time it has become a problem in metal building applications. I’ve seen rust through in five years but most commonly in ten to fifteen years. When you finally notice it it is way too late. All the foam has to be removed then sheets and in some cases purlins and girts if they are rusted through.

Check with your building supplier to find out if the warranty is void if spray foam is applied. Some metal suppliers will void their warranties and I write it into all my contacts now.

Now I know that there will be lots of replies about how someone had their building spray foamed and they love it. I get it and I bet it transformed their building into a perfect place to work all year around. Foam damage seems to be some what selective. They may never have a problem but why take a chance. Fiberglass can be installed for quite a bit less money and provide nearly the same results.
 

kj_mustang

Well-known member
Joined
Feb 9, 2011
Messages
1,213
Location
Harrisonburg, VA
There are too many other factors involved; ie: types of spray foam used, thickness of foam applied to achieve water vapor barrier for the geographic location of the structure, hvac conditioned vs nonconditioned interior space, to make a blanket statement that spray foam will cause metal corrosion.
 
To avoid these ads, REGISTER NOW!

readhead

Well-known member
Joined
Dec 8, 2012
Messages
6,187
Location
Durango, Co.
How about if I say it happens a lot in buildings with spray foam and I have never seen the problem with other kinds of insulation. I’ve been selling, erecting and repairing metal buildings for twenty years.
 

kj_mustang

Well-known member
Joined
Feb 9, 2011
Messages
1,213
Location
Harrisonburg, VA
People who don't know enough about the insulation they are using and the environmental factors of the structure have been causing issues for many decades, such as finished basement walls with mold and rot.
 

readhead

Well-known member
Joined
Dec 8, 2012
Messages
6,187
Location
Durango, Co.
That is a long conversation since most tube steel buildings are not erected with sealing in mind. I will hit the major points.

Is there a vapor barrier under the slab? If not you may be getting some moisture migrating through the slab. A way to find out how much moisture is to tape a one foot square piece of plastic on the slab and see what accumulates on the bottom of the plastic after 24-48 hours.
Since there is no location in your profile I don't know if you are in a heating or cooling area. We will assume cooling since you asked about humidity. You will not get rid of it but you can manage it. The obvious answer is air conditioning but lets look at insulation and ventilation.
Insulating with rigid foam or fiberglass will be the most cost effective. Ventilation in the form of an exhaust fan and intake louver in opposite ends of the building mounted as high as you can should move the hot moist air out of the building. In some cases you will want to leave the intake closed and just operate the exhaust fan to remove the warm air.

Insulation works to keep the warm in as well as out so it may take a while to work out the best management. If you are not worried about staying cool just open the doors and let the dew point even out and you will not have any condensation. It my take a while but you will figure it out.
 

Slowbuilder

Well-known member
Joined
Mar 14, 2016
Messages
265
Location
Chandler, AZ
Another vote for SilverCote. I believe they provide post-construction kits as well, and they also supply rockwool insulation, which I believe is slightly better R-value than fiberglass, and is easier to work with (less irritation to the skin)
 

Gunfixr

Well-known member
Joined
Feb 9, 2021
Messages
677
Location
behind the house
That is a long conversation since most tube steel buildings are not erected with sealing in mind. I will hit the major points.

Is there a vapor barrier under the slab? If not you may be getting some moisture migrating through the slab. A way to find out how much moisture is to tape a one foot square piece of plastic on the slab and see what accumulates on the bottom of the plastic after 24-48 hours.
Since there is no location in your profile I don't know if you are in a heating or cooling area. We will assume cooling since you asked about humidity. You will not get rid of it but you can manage it. The obvious answer is air conditioning but lets look at insulation and ventilation.
Insulating with rigid foam or fiberglass will be the most cost effective. Ventilation in the form of an exhaust fan and intake louver in opposite ends of the building mounted as high as you can should move the hot moist air out of the building. In some cases you will want to leave the intake closed and just operate the exhaust fan to remove the warm air.

Insulation works to keep the warm in as well as out so it may take a while to work out the best management. If you are not worried about staying cool just open the doors and let the dew point even out and you will not have any condensation. It my take a while but you will figure it out.
I thought I had put my location in my profile, I will check that.
However, i'm in virginia, just a bit east and South of richmond.
I highly doubt anything was put under the slab, I was not present when it was poured. I did seal the top. Moisture collects on most things, particularly metal ones. My lathe and mill look like hell now, tools rusted, plastic handles have that white mold on them.
I was planning a wood stove in the back, centered, and an exhaust fan up front at the peak. It has that bubble wrap type insulation in the roof, done when the building was put up.
 

kj_mustang

Well-known member
Joined
Feb 9, 2011
Messages
1,213
Location
Harrisonburg, VA
In your location with the high humidity levels in the summer and lack of a vapor barrier under the slab, I seriously doubt you will ever seal it up enough to keep interior moisture levels down without using some type of dehumidifying device.
 

kj_mustang

Well-known member
Joined
Feb 9, 2011
Messages
1,213
Location
Harrisonburg, VA
2" closed cell spray foam will give you a water vapor barrier on the structure. But every time the door is opened, in comes the humidity and you will get some moisture up through the slab. Insulate and install a/c. Types of both of those depends on the money you want to spend.
 

FO876

New member
Joined
Apr 15, 2018
Messages
1
Location
Middle TN
Maybe not what you want to hear, but my own metal frame metal siding 30x40x12 was sprayed with closed cell foam. seals great and while not the cheapest method it is probably the fastest and easiest after construction is completed.
How's it holding up? How many years old? Any negative signs of corrosion anywhere???




Purchased a home with a 22'x25'x10' metal building (uses 2.5" square tubing), the spacing varies from 60"OC to less than that. So as a result, I'm not entirely sure how to go about finishing off the inside. My latest idea is maybe using 1x4's as girts inside so I have something to nail or screw paneling to?

Anyone with experience with these types of buildings, feel free to chime in with any advice!

Will they support the weight of running the 1x4's and paneling up to 8'????

I'm also interested in adding side sheds, was thinking 2x6 header screwed up top along the side then running 2x6x10 or 12 possibly every 24"OC. But again, unsure if those 2.5" square tubing can handle the added weight and not sure who I can contact to find out?!?!?

Any help would be great! TIA!
 
Last edited:

texasfiremedic

Well-known member
Joined
Oct 5, 2013
Messages
396
Location
Canton. TX
How's it holding up? How many years old? Any negative signs of corrosion anywhere???




Purchased a home with a 22'x25'x10' metal building (uses 2.5" square tubing), the spacing varies from 60"OC to less than that. So as a result, I'm not entirely sure how to go about finishing off the inside. My latest idea is maybe using 1x4's as girts inside so I have something to nail or screw paneling to?

Anyone with experience with these types of buildings, feel free to chime in with any advice!

Will they support the weight of running the 1x4's and paneling up to 8'????

I'm also interested in adding side sheds, was thinking 2x6 header screwed up top along the side then running 2x6x10 or 12 possibly every 24"OC. But again, unsure if those 2.5" square tubing can handle the added weight and not sure who I can contact to find out?!?!?

Any help would be great! TIA!