Alright here's a new one for me. So yesterday I went out to Bum-f$%@ nowhere Colorado to start one of my idle compressors and noticed some odd voltage numbers on my pre-startup checks.
480V 3phase dedicated service from POCO , no loads, main breaker open, readings taken from line side of breaker. POCO meter shows no phase loss.
Here's what I got:
L1-L2: 283V
L2-L3: 5V
L1-L3: 288V
L1-GND: 286V
L2-GND: 0V
L3-GND: 4V
So then I run down the road to another site that I know has good power, (also different utility) Just to verify my meters and sanity. Meters check out so I go back to the compressor site to double check my original readings. This time around I get the numbers below:
L1-L2: 204V
L2-L3: 38V
L1-L3: 166V
L1-GND: 286V
L2-GND: 98V
L3-GND: 128V
The only thing I can think is that there is maybe a ground fault between the pole and my main breaker and the conduit is probably full of mud and water as well. Anyone have any other ideas?
480V 3phase dedicated service from POCO , no loads, main breaker open, readings taken from line side of breaker. POCO meter shows no phase loss.
Here's what I got:
L1-L2: 283V
L2-L3: 5V
L1-L3: 288V
L1-GND: 286V
L2-GND: 0V
L3-GND: 4V
So then I run down the road to another site that I know has good power, (also different utility) Just to verify my meters and sanity. Meters check out so I go back to the compressor site to double check my original readings. This time around I get the numbers below:
L1-L2: 204V
L2-L3: 38V
L1-L3: 166V
L1-GND: 286V
L2-GND: 98V
L3-GND: 128V
The only thing I can think is that there is maybe a ground fault between the pole and my main breaker and the conduit is probably full of mud and water as well. Anyone have any other ideas?