Generator interlock for only 1 panel of 2 main panel service

neftci

New member
Joined
Sep 13, 2013
Messages
3
Location
Texas
Newbie here. Apologize if I should have built on a previous thread. I have read previous generator interlock threads about those trying to power both panels of a 2 panel 320 amp split service, with one generator. I have 2 main panels as well, but for me, all the loads I want to power are one panel. So any reason given my setup shown in the pictures that I cannot just use one interlock on that panel? I would have a 30 amp generator inlet outlet installed outside and run into the panel and connected to a 30 amp generator breaker in the correct position for the interlock.

All the previous threads seem to suggest that this fine but want to check before I proceed. My panels are fed by the trough shown in the picture and although I did not want to open it up, I assume the panel's neutrals and grounds are joined based on continuity tests I did at the panels.

Also question about the neutral. Since the interlock does not switch the neutral, why does this not create a parallel neutral situation where the generator power can flow either back to the generator via the generator circuit and/or out to the transformer via the service neutral?

Thank you in advance

IMG_4775.JPG I

IMG_4776.JPG
 
To avoid these ads, REGISTER NOW!

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,317
Location
Coronado, CA
Yes, you are correct. The shared neutral can become energized, this was demonstrated to me a long time ago in a place far away, but it is still true.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,317
Location
Coronado, CA
After a couple of minutes thought, I realized that in the US and Canada current practice is that Neutrals are grounded at the Service Entrance.
 
To avoid these ads, REGISTER NOW!

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
20,274
Location
Northern Virginia
My previous house was 400A service with two separate electric panels like yours (double tapped meter).

The generator served only one panel like yours with the most critical loads. Was kind of neat as lights on the other panel would come on when utility power came back so we knew it was time to turn off the generator.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
Newbie here. Apologize if I should have built on a previous thread. I have read previous generator interlock threads about those trying to power both panels of a 2 panel 320 amp split service, with one generator. I have 2 main panels as well, but for me, all the loads I want to power are one panel. So any reason given my setup shown in the pictures that I cannot just use one interlock on that panel? I would have a 30 amp generator inlet outlet installed outside and run into the panel and connected to a 30 amp generator breaker in the correct position for the interlock.

All the previous threads seem to suggest that this fine but want to check before I proceed. My panels are fed by the trough shown in the picture and although I did not want to open it up, I assume the panel's neutrals and grounds are joined based on continuity tests I did at the panels.
yes that will be fine....
Also question about the neutral. Since the interlock does not switch the neutral, why does this not create a parallel neutral situation where the generator power can flow either back to the generator via the generator circuit and/or out to the transformer via the service neutral?

Thank you in advance
Contrary to popular misperception, electricity returns to its source.

So any current from the generator on the neutral wont be going back to the transformer, because the source is the generator...
Yes, you are correct. The shared neutral can become energized, this was demonstrated to me a long time ago in a place far away, but it is still true.
but that isnt even a concern since the neutral return current will go back to the generator NOT the transformer... furthermore, the neutral in a main service panel is at the same potential as the ground, so there is no potential for shock
 
OP
N

neftci

New member
Joined
Sep 13, 2013
Messages
3
Location
Texas
yes that will be fine....

Contrary to popular misperception, electricity returns to its source.

So any current from the generator on the neutral wont be going back to the transformer, because the source is the generator...

but that isnt even a concern since the neutral return current will go back to the generator NOT the transformer... furthermore, the neutral in a main service panel is at the same potential as the ground, so there is no potential for shock
Thank you for your reply
 