I replaced the receptacle, plugged in the freezer and the circuit has stayed
up for over 24hrs. So either the receptacle was bad (no signs of that) or
something I did in the process of replacing it fixed the problem.
It's in a finished area of the basement, so it looks like any other part of the house.
Thanks to everyone for your advice and comments.
Here's the long version:
20A circuit in finished basement area with 7 duplex outlets. Freezer plugged
into an outlet in the middle of the circuit. Lamp plugged into the last outlet on the
circuit.
Circuit breaker started tripping at various times.
I unplugged the freezer and the lamp, no change (NC).
I replaced the breaker, NC.
I located the first outlet and disconnected the downstream wires, NC.
I disconnected the wires from the first outlet, circuit did not go down (4 day test).
Indicates bad outlet.
I replaced the outlet, connected the downstream wires, plugged in the freezer,
circuit has been up over 24 hrs. Fingers crossed, I hope this is the end of the
story.