Crouse Hinds circuit breaker x-ref

nbpt100

Well-known member
Joined
Oct 19, 2016
Messages
2,304
Location
Massachusetts
I have a Crouse-Hinds 15 amp 1/2" wide breaker running one 75 watt outdoor light that keeps tripping every couple of days. The wiring in the box looks fine and the fixture looks ok as well. I am at the point where I suspect the breaker is going bad. I have read a number of conflicting and confusing posts about acceptable replacements. I have not gone to the electrical supply house yet and ask. It is a bit of a drive so I thought I would try to get some experienced help here first to see what the experts here can share.
 
Last edited:
To avoid these ads, REGISTER NOW!

GJK1981

Member
Joined
Mar 13, 2022
Messages
22
is this a photo cell controlled light? Or is it powered through a switch? Or are you using the breaker for the switch. If it’s photo electric it may be an issue wherever that junction is. It may be going bad? Is it in a wet location? Water will cause it to trip easily. Maybe if it’s on a switch and made up in a metal box somethings shorting out.?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
The inside of the panel should list replacements. Otherwise, the manufacturer is the only source of that info. If the panel is so old that breakers are not available, you may be stuck.

I agree on confirming the breaker as bad by swapping.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
Crouse-Hinds & Challenger twins were the only twin breakers that allowed 240V, well GE still does but they are and only work for GE products only, so if the OP's were part of a multiwire circuit it will a problem, Crouse-Hinds was the only one allowing competitive makes for breakers, if the label in intact ITE, now Siemens, and Bryant BR, now Eaton BR were allowed, other option is Eaton CL, the CL is UL classified for most competitive panels.


 
OP
N

nbpt100

Well-known member
Joined
Oct 19, 2016
Messages
2,304
Location
Massachusetts
Thanks for the replies. This was a few months ago now. I ended up replacing the breaker and it solved all of the issues. The supply house I use had a very knowledgable salesman and cross refed a good replacement breaker from another brand. It looked nearly identical to the CH.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
The inside of the panel should list replacements. Otherwise, the manufacturer is the only source of that info. If the panel is so old that breakers are not available, you may be stuck.

I agree on confirming the breaker as bad by swapping.
except crouse-hinds is no longer around so the panel label means nothing. before they were acquired by siemens, crouse-hinds bought murray.

murray has listed breakers for crouse-hinds panels so murray should be used....
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
Crouse-Hinds & Challenger twins were the only twin breakers that allowed 240V, well GE still does but they are and only work for GE products only, so if the OP's were part of a multiwire circuit it will a problem, Crouse-Hinds was the only one allowing competitive makes for breakers, if the label in intact ITE, now Siemens, and Bryant BR, now Eaton BR were allowed, other option is Eaton CL, the CL is UL classified for most competitive panels.


murray should have listed breakers as well
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
except crouse-hinds is no longer around so the panel label means nothing. before they were acquired by siemens, crouse-hinds bought murray.

murray has listed breakers for crouse-hinds panels so murray should be used....
I did say "should" and "may", to be fair

:)
 