Any reason my ground rods can't be in the same trench as my service? Not layed horizontal but straight down with a foot or so of cover over the top? Doing so would save me 10ft or so of 4ga wire with how my job is layed out.
 
To avoid these ads, REGISTER NOW!
To avoid these ads, REGISTER NOW!

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Ground rods are #6 copper, you can run bigger, but you are wasting money. Your Grounding electrode conductor however is sized per your size of your ungrounded service entrance conductors. You would use table 250.66 of the NEC to find your size. There are columns for both copper and aluminum. What size is your service entrance conductors?
 
OP
H

haveissues

Well-known member
Joined
Feb 9, 2011
Messages
379
Location
Hudson Valley NY
Ground rods are #6 copper, you can run bigger, but you are wasting money. Your Grounding electrode conductor however is sized per your size of your ungrounded service entrance conductors. You would use table 250.66 of the NEC to find your size. There are columns for both copper and aluminum. What size is your service entrance conductors?
It's a meter on posts next to my transformer so I only have 2 ground rods. I have to re-read the utilities handbook. I feel like they require #4 for services greater than 200 to ground rods but I may have read that incorrectly.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
It's a meter on posts next to my transformer so I only have 2 ground rods. I have to re-read the utilities handbook. I feel like they require #4 for services greater than 200 to ground rods but I may have read that incorrectly.
If that what your handbook says, then that is what you go by. The NEC only requires a #6
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,992
Location
Central Iowa
Some places claim to require a #4 if any of the copper is exposed outside. They are afraid a #6 will get destroyed by a weed eater. I've never checked for an amendment, just gone ahead and done it.
 