So as of yesterday I have a new 320 amp service and 200 amps running to the new shop but have a question on bonding a 3r box. Until yesterday I had a meter pan back to back with a 200 amp panel at my house (meter pan outside, 200 amp panel inside). I moved my meter to a pedestal and now have a 200 amp panel at the shop and the same 200 amp panel I had before at the house but replaced the meter pan with a slightly larger 3r box that I am using as a splice box. 2" PVC conduit comes in to that box from underground and 2" pvc conduit comes out of the back and in to my indoor panel.
Here is my question-there was no bonding in the meter pan that I removed. I spliced the 4/0, 4/0, 2/0 with polaris connectors where the meter would have been. Should that 3r box be bonded and what wire gauge? Hope that makes sense...
I am also surprised the meter pan is not bonded to ground. Whoever did the work was no amateur as the breaker panel is very very neat and tidy. Whoever did it must have been down right **** (not a bad thing, I like neat).
Here is my question-there was no bonding in the meter pan that I removed. I spliced the 4/0, 4/0, 2/0 with polaris connectors where the meter would have been. Should that 3r box be bonded and what wire gauge? Hope that makes sense...
I am also surprised the meter pan is not bonded to ground. Whoever did the work was no amateur as the breaker panel is very very neat and tidy. Whoever did it must have been down right **** (not a bad thing, I like neat).