I want to run wire back to my house to control 2 lighting circuits on a detached shed. The shed will be fed with 20a MWBC, so no panel in the shed. Just lighting and a couple receptacles with a DP 20a toggle switch for the disconnect.
To keep the 20a breaker rating kosher, I'll run #12. Wire will be THWN, underground in pvc conduit. Likely 1/2"
The switches will both be three way, and likely just simple switches that don't need a neutral, although I would like to have one in case I do something different down the road.
I can pull a single neutral and ground to cover both switches, correct? Other than that, I know I'll need two hots for each, so 6 wires total, which would put me at 28% fill in 1/2
To keep the 20a breaker rating kosher, I'll run #12. Wire will be THWN, underground in pvc conduit. Likely 1/2"
The switches will both be three way, and likely just simple switches that don't need a neutral, although I would like to have one in case I do something different down the road.
I can pull a single neutral and ground to cover both switches, correct? Other than that, I know I'll need two hots for each, so 6 wires total, which would put me at 28% fill in 1/2