LED Dimmer question for 4k lights

craigibc

Well-known member
Joined
Nov 17, 2010
Messages
265
Location
Western New York
I picked these lights up at the depot and I cannot figure out how to wire them for a dimmer. It has 2 separate sets of wires and not sure how to hook up the dimmer. Anyone with any experience? Google did not help me much in my search.
 

Attachments

  • IMG_4929.jpeg
    IMG_4929.jpeg
    119.6 KB · Views: 43
  • IMG_4927.jpeg
    IMG_4927.jpeg
    153.6 KB · Views: 37
  • IMG_4926.jpeg
    IMG_4926.jpeg
    176.9 KB · Views: 39
To avoid these ads, REGISTER NOW!
OP
C

craigibc

Well-known member
Joined
Nov 17, 2010
Messages
265
Location
Western New York
So I have 8 lights in the shop so I connect all these together with a purple and gray wire and then run the last set to the dimmer. Interesting.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,893
Location
NW Iowa
So I have 8 lights in the shop so I connect all these together with a purple and gray wire and then run the last set to the dimmer. Interesting.
That's right. The dimming is completely separate from the 120v circuit.
 
OP
C

craigibc

Well-known member
Joined
Nov 17, 2010
Messages
265
Location
Western New York
any recommendation on a wire to use for the dimmer feature. I checked the local hardware store and I am looking around 69 cents per foot. I need around 160ft of wire. Any recommendation on a wire to use to carry the dimmer capability?
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
any recommendation on a wire to use for the dimmer feature. I checked the local hardware store and I am looking around 69 cents per foot. I need around 160ft of wire. Any recommendation on a wire to use to carry the dimmer capability?
What kind of wire did you use to wire the 120 volt to the fixtures. A NM-b or MC cable. It needs to have a 600 volt rated insulation since it will be inside the fixture
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,996
Location
Thousand Islands NYS
If it's in the same compartment, has to have same protection. If your fixtures have a barrier - I think rare but not sure how much it changed - not required.

If you have no wiring installed, consider NM 14-2-2 (or 12-2-2) with power and data in one jacket. Somewhat pricey but a little less install work.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
But why would that matter for the control circuit? Honest question, not busting stones
I guess I will retract what I said, If its in the same raceway or cable assembly as the power conductors then it would have to have the same insulation rating , which most likely would be 600 volt. But a separate cable like a 18/2 thermostat wire would have to have a insulation rating of not less the voltage in the fixture
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
I guess I will retract what I said, If its in the same raceway or cable assembly as the power conductors then it would have to have the same insulation rating , which most likely would be 600 volt. But a separate cable like a 18/2 thermostat wire would have to have a insulation rating of not less the voltage in the fixture
So if one used any wire rated higher than 600v, everything would have to be rated to that level?
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
As mentioned above, I would recommend a single cable with everything in it for ease of installation. Especially if the power is originating from the same box that the dimmer is in.

Edit: after reading up on this, if using a single cable assembly, it would have to be the MC cable identified for this. A 14/2/2 NM-b would not comply
 
Last edited:

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Came across this

 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
2017 NEC 300.3 (C)
(C) Conductors of Different Systems.
(1) 1000 Volts, Nominal, or Less. Conductors of ac and dc circuits, rated 1000 volts, nominal, or less, shall be permitted to occupy the same equipment wiring enclosure, cable, or race‐way. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
2017 NEC 300.3 (C)
(C) Conductors of Different Systems.
(1) 1000 Volts, Nominal, or Less. Conductors of ac and dc circuits, rated 1000 volts, nominal, or less, shall be permitted to occupy the same equipment wiring enclosure, cable, or race‐way. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.
So the rating of the wiring doesn't all need to be the same. You can have a mix of 600v and 150v as long as nothing is more than 150v
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
2017 NEC 300.3 (C)
(C) Conductors of Different Systems.
(1) 1000 Volts, Nominal, or Less. Conductors of ac and dc circuits, rated 1000 volts, nominal, or less, shall be permitted to occupy the same equipment wiring enclosure, cable, or race‐way. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.
That article does not apply when the LED driver is identified as a class 2 device, as noted in the informational note #1 in 300.3(C)(1). Which it is in this case by the picture the OP posted. This information would be found in article 725.136 which says class 2 conductors has to be isolated from power conductors unless permitted by 725.136(B) though (I). Pretty much has to have a barrier or a 2 inch separation. This gets confusing because they make a MC cable that has all the conductors in it. Read this article


 
Last edited:

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
So the rating of the wiring doesn't all need to be the same. You can have a mix of 600v and 150v as long as nothing is more than 150v
Not in this case, because this is a class 2 circuit. It would need a 2 inch separation or barriers. It all has to do about what class the control circuit is, sometimes the insulation rating has nothing to do with it. I was wrong when I first quoted this
 
Last edited:

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Sorry to everyone for making this confusing, I to had to read up on this. So to answer the OPs question about what kind of wire to use, If your using a single cable assembly for power and control, then it would have to be MC cable identified for this. If using a separate cable, I would suggest an in wall rated 18/2 conductor cable. Keep it at least 2 inches away from the power conductors in the fixture and if the dimmer is in a box with power wiring, use barriers.

They sell this in different lengths

 

pbon

Well-known member
Joined
May 14, 2017
Messages
3,498
I bought 250’ of 16-2 or 18-2 600V rated when I did my 30 lights on 7 switches. In hindsight I would have been happy with 4-5 switches.
 

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,467
Location
USA
any recommendation on a wire to use for the dimmer feature. I checked the local hardware store and I am looking around 69 cents per foot. I need around 160ft of wire. Any recommendation on a wire to use to carry the dimmer capability?
Run your purple and gray wires to the junction box in the ceiling. Install a Lutron Vive Powpak. Then use wireless Pico switches wherever you want them.
https://www.lutron.com/TechnicalDocumentLibrary/367-2597_Vive_Design_Guide.pdf

CD
 

pbon

Well-known member
Joined
May 14, 2017
Messages
3,498
As long as you keep the doorbell wire out of the box with the 120V wire. You can do completely separate dimmer circuit and switch. The part that I don’t understand is that the doorbell wire is presumably connected to the purple and gray inside the light fixture. I would think the purple and gray need to come out so they are separated from the 120 before being connected to the doorbell wire.
 