Connecting 4g wire to 12g wire

Paulski

Well-known member
Joined
Sep 29, 2017
Messages
119
I am trying to figure out how to connect 4g wire to 12g wire in house wiring

Situation:

Looks like someone was planning to install a sub panel in the garage, but never finished-
-The sub panel is in the garage wired with both hots to the breaker legs, and has a neutral and ground to there own bus bars. A 20 amp breaker in the sub panel feeds 12/2 romex to power the garage. There are no grounding rods wired to the sub panel
-The 4 4g wires go in to a 1 1/2" PVC conduit that goes to under the house where the wires exit out the end of the conduit and are lying on the ground connected to 12/2 romex with wire kearneys
-The 12g romex goes up the wall and ends at the breaker panel to a 20amp breaker

I do not need a sub panel or 240v in this garage and want to make it safe/to code. I do not think I can pull new wire though the conduit, it has to many bends buried in pretty new concrete down the driveway. I'm guessing 5 90* bends

Plan:
-Gut the internals of the sub panel and just use it as a J box
-Connect a J box to the conduit under the house and connect the 4g wire to the 12g wire in the box
-Leave the 2nd hot wire disconnected in both boxes in case its needed later

How do I connect the 4g wire to the 12g wire correctly?
I was thinking of screwing a 3 wire terminal block into the J box under the house and one in the gutted sub panel box. Do they make terminal blocks that will take 4g wire on one side and 12g wire on the other side? Also, do they make some sort of plastic cover that can be screwed over the terminal block - I was think for extra safety if someone was to open the door to the gutted sub panel and stick there hand in with a live circuit. Or I could put in the breaker cover plate as an extra guard too

Or is a kearney wrapped in electrical tape acceptable in a J box for the hot, neutral and ground wire?

Edit - So I found this to use as a terminal block
But is it ok to install in a J Box?
 
Last edited:
To avoid these ads, REGISTER NOW!

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,418
Location
Western North Carolina
Do you have to gut the garage panel?
Might be better to have a breaker in there so you do not have to go to the main panel when the breaker flips.
 
OP
P

Paulski

Well-known member
Joined
Sep 29, 2017
Messages
119
Where is there nm outdoors?
The NM is in the crawl space

Do you have to gut the garage panel?
The panel isn't permitted and is missing the 2 grounding rods. The garage is also dry walled - I'm figuring its cheaper/easier to gut it and add the terminal blocks than to run ground cable through the walls and add grounding rods.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,894
Location
Richmond, VA
Is the panel on an outside wall? You could go down inside the wall and then out with an LB for your ground wire.

Even if you don't need the service now, you are so close to having a good setup. Seems odd to throw it away for a single 20a circuit
 
To avoid these ads, REGISTER NOW!

Fasthotrod

Well-known member
Joined
Dec 14, 2015
Messages
218
Location
Oklahoma
I do not think I can pull new wire though the conduit, it has to many bends buried in pretty new concrete down the driveway. I'm guessing 5 90* bends

Just wanted to mention that if it indeed has five, 90 degree bends, it's not to Code.

Per the NEC:

“There shall not be more than the equivalent of four quarter bends (360 degrees total) between pull points, for example, conduit bodies and boxes.”
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,593
Location
Fullerton, CA
Getting it permitted with the conduit inaccessible may be difficult as they can't verify depth
I just find it "curious" that the first thing mentioned wrong was the panel didn't have a permit.
The easiest way to splice the wires together would with insulated taps (like NSI's Polaris)
 
Last edited:

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,775
Location
NW Iowa
Getting it permitted with the conduit inaccessible may be difficult as they can't verify depth
Is that even a thing? I've hardly ever left a trench open for inspection. I wouldn't want to leave my equipment sitting on a job for a couple days just waiting, need to be moving on to the next one.
 

ycgoat

Well-known member
Joined
Mar 28, 2020
Messages
971
Location
S.E. Va
I am lazy and did not read the entire post but the easy old school method of connecting #12 to #4 is a split bolt then if its current carying taped with 3 layers of rubber and 3 layers of vinyl
 

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,418
Location
Western North Carolina
Is that even a thing? I've hardly ever left a trench open for inspection. I wouldn't want to leave my equipment sitting on a job for a couple days just waiting, need to be moving on to the next one.
Yup, I was not allowed to close the trench when I ran power to the garage until the inspector verified the depth.
Maybe it was because it went under two driveways and minimum depth changes with the type of surface of the driveway.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,894
Location
Richmond, VA
Is that even a thing? I've hardly ever left a trench open for inspection. I wouldn't want to leave my equipment sitting on a job for a couple days just waiting, need to be moving on to the next one.
Definitely. But you should be able to get a trench inspection pretty quickly. I have also heard of people leaving a scrap piece of conduit vertically in the trench so an inspector can run a tape measure down to the pipe
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,705
Location
Fargo, ND
I am still trying to wrap my head around the concept that you have a sub panel, in the garage, wired in 4 ga, and you want to get rid of it? If I understand the house end is wired to 12 ga?

Why not just finish up the panel and get it wired in properly? Or am I missing something? In five years you might want to charge your EV, then you will be buying a panel and ripping out the mess you make now.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Is that even a thing? I've hardly ever left a trench open for inspection. I wouldn't want to leave my equipment sitting on a job for a couple days just waiting, need to be moving on to the next one.
We are required to get a ground cover inspection
 