Patching drywall after panel replacement?

Mike1903

Well-known member
Joined
Jan 16, 2021
Messages
139
Location
Suburbs
Picture is attached.
Any future wires will be coming through the bottom. Any advise before I patch up the drywall and finish it? Should I leave a small gap just below the panel to be able to install clamp connectors?

thx
 

Attachments

  • 89A4AA1C-71BD-4CA8-BFCF-4EFD45A7839F.jpeg
    89A4AA1C-71BD-4CA8-BFCF-4EFD45A7839F.jpeg
    321.3 KB · Views: 160
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
Put PVC conduit into the crawl space, not as cheap as it used to be, but a sick of conduit, terminal adapter, locknut, & a plastic bushing is still cheaper then opening up the wall & patching it. Be generous with the pipe size smaller pipe will fill quickly when using NM cable,"Romex®", if a lot of circuits are planned, 2" would not hurt.
 

James-W

Well-known member
Joined
Feb 3, 2013
Messages
12,432
Location
Southeastern Wisconsin
In my garage I put a removable thin plywood panel above the service panel so that if needed I can run new electrical cable up to the second floor and wire it into the panel. I seriously doubt I will even need to do that, but the point is that by planning ahead I have the capability to do it if I need to. I highly recommend that you do something similar so that in the event you do need to run additional circuits you will be able to do so without having to do a major renovation.

I am big fan of being "proactive" even when it means spending a bit more money now rather than having to spend a lot of money later because I couldn't see the forest for the trees.
 

ycgoat

Well-known member
Joined
Mar 28, 2020
Messages
971
Location
S.E. Va
You can fight romex connectors with the wire into the panel through a 1/2” gap, its a pain and usually ends up as 1” gap when Your done. Typically now, I will put a connector on the wire before I fish it into the panel, if accessible, or put the connector inside the panel, if I have no other way.
 

Git

Well-known member
Joined
May 18, 2008
Messages
6,895
Location
S Cal
In the future, they make a metal 'j bead' that you can use to cover up the cut edges and give you a nice straight line next to the panel. (usually you would install it before the panel goes in)

Regarding future connections - I would just run some smurf tubing either up into the attic or down into the wall below so you can access it later. (Use a male adapter to bring it into the panel)


T22-044.jpg T22-045.jpg T22-046.jpg
 

ycgoat

Well-known member
Joined
Mar 28, 2020
Messages
971
Location
S.E. Va
Yes Alfredeneuman, I was referring to adding a circuit to an existing panel, but it is a good point for the OP, though I have never heard of it being enforced at the panel, but I do not do the drywall.
 

Syberia

Well-known member
Joined
Jan 13, 2014
Messages
1,451
Location
Perris, CA
Add an access panel slightly above/below, wherever your wires come in, and hang a picture over it. I have done this with both electrical panels in my house and it makes adding things later super easy.
 

ycgoat

Well-known member
Joined
Mar 28, 2020
Messages
971
Location
S.E. Va
Quick note about the Blue flexible non metallic tubing suggested above. It is required to be continuous from termination point to termination point and is not supposed to just stub out into an attic or crawl space. You could terminate it in a box, or use a different type of flexible conduit.
 

Git

Well-known member
Joined
May 18, 2008
Messages
6,895
Location
S Cal
Quick note about the Blue flexible non metallic tubing suggested above. It is required to be continuous from termination point to termination point and is not supposed to just stub out into an attic or crawl space. You could terminate it in a box, or use a different type of flexible conduit.
I am not an electrician, but please explain why you think that is the case?
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
NEC article 314.21

Only in combustible materials.
NEC 314.21
Repairing Noncombustible Surfaces. Noncombustible
surfaces that are broken or incomplete around boxes employ‐

ing a flush-type cover or faceplate shall be repaired so there
will be no gaps or open spaces greater than 3 mm (1∕8 in.) at the
edge of the box
 
To avoid these ads, REGISTER NOW!

ycgoat

Well-known member
Joined
Mar 28, 2020
Messages
971
Location
S.E. Va
I am not an electrician, but please explain why you think that is the case?
I believe it is article 362.30 of the NEC. 362.30 SecuringandSupporting.ENTshallbeinstalled as a complete system as provided in Article 300 and shall be securely fastened in place and supported in accordance with 362.30(A) and (B).
 

Git

Well-known member
Joined
May 18, 2008
Messages
6,895
Location
S Cal
GIT, I got hit on it in an inspection by the city inspector
OK - but wouldn't it depend on where you live? For example, Chicago requires steel conduit for all residential wiring, even in the walls
 

ycgoat

Well-known member
Joined
Mar 28, 2020
Messages
971
Location
S.E. Va
The NEC is used in all cities and is the minimum, so places like Chicago may say no ENT, but not allow you to install it contrary to the NEC code.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,317
Location
Coronado, CA
I have a metal access plate covering the space between the top of my panel in the house to the ceiling in my laundry room, it is painted wall color.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,963
Have you ever seen a surface mount cover used with a drywall or plaster finish? It looks like :poop: anyway
I stayed in hotel this last week that had one in the room. It was painted to match the wall, and didn't look that bad. I mean, I wouldn't have had it my house, but I doubt my wife noticed it.
 

EngineerNate

Well-known member
Joined
Oct 19, 2019
Messages
206
Location
Bristol, TN

Put one of these in, paint it to match the wall.

If you stub down with conduit, you can generally just put a bushing on the end of the conduit if it's stubbing down/up inside a wall. If it's surface mounted and penetrates a ceiling you generally have to have a box on the other side to terminate it into.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
362.30 SecuringandSupporting.ENTshallbeinstalled as a complete system as provided in Article 300 and shall be securely fastened in place and supported in accordance with 362.30(A) and (B).
You missed an exception >
Exception No. 3: For concealed work in finished buildings or prefinished wall panels where such securing is impracticable, unbroken lengths (without coupling) of ENT shall be permitted to be fished
 

ycgoat

Well-known member
Joined
Mar 28, 2020
Messages
971
Location
S.E. Va
You missed an exception >
Exception No. 3: For concealed work in finished buildings or prefinished wall panels where such securing is impracticable, unbroken lengths (without coupling) of ENT shall be permitted to be fished

Yes it can be fished and not secured in the void, but it is still supposed to be ran as a continuous run from termination to termination, but it not to be fished through a wall and just end with the cables continuing on.
 
Last edited:

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
but it not to be fished through a wall and just end with the cables continuing
That's not what the OP is talking about. The placed where fished will immediately above and connected to the panel. If he puts a box on the other end that would be the other termination.
 