Anyone using an interlock for their generator?

gayler

Well-known member
Joined
Sep 22, 2011
Messages
3,282
Location
Lakin Kansas
A transfer switch is $700 dollars. Interlock is only 40 or so. Why spend all that money if an interlock will work?
 
To avoid these ads, REGISTER NOW!

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,674
Location
Long Island
The transfer switch may be automatic, and may come with programming to exercise your generator, etc.
The interlock will require you to step outside into whatever weather nature has provided to get the generator running.
 

ycgoat

Well-known member
Joined
Mar 28, 2020
Messages
971
Location
S.E. Va
I have put in few here in Va, they are for portable generators, the ATS would be for a fixed/permanent generator. There is some language in the code that could be interpreted as not allowing them so a phone call to the local inspector is a good idea, but I have not had any deny it, and the interlock is widely available
 

D45

Well-known member
Joined
Mar 21, 2014
Messages
4,836
Location
NW INDIANA
Don't you need a panel with an open circuit/slot?

If you panel is full though, what options are there?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,920
Location
Richmond, VA
Don't you need a panel with an open circuit/slot?

If you panel is full though, what options are there?
Two slots, closest to the main.

You move stuff to tandems or install a sub. Tandems are easy, if your panel is rated for them. Small subs are cheap, too
 

ycgoat

Well-known member
Joined
Mar 28, 2020
Messages
971
Location
S.E. Va
There is always more than 1 way to do anything, some options could be a new larger panel or add a sub panel. Besides space you also have to have a main breaker and they have to make an interlock to fit your panel
 

D45

Well-known member
Joined
Mar 21, 2014
Messages
4,836
Location
NW INDIANA
I have a 200AMP Square D............all circuits are full
 

Attachments

  • panel1.JPG
    panel1.JPG
    11.9 KB · Views: 96
  • panel.jpg
    panel.jpg
    12.6 KB · Views: 96

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,073
Location
Modesto, CA
A transfer switch is $700 dollars. Interlock is only 40 or so. Why spend all that money if an interlock might work?
fixed it for ya :thumbup:

too many variables to be able to definitively conclude that an interlock will work
 
Last edited:
OP
G

gayler

Well-known member
Joined
Sep 22, 2011
Messages
3,282
Location
Lakin Kansas
fixed it for ya :thumbup:

too many variables to be able tp definitively conclude that an interlock will work
I have an external panel. 8 slots, no main breaker. I will change to a panel with a main breaker. I would like to stay with Square D homeline. I would be using a 5KW generator for emergency use only, so only furnace blower, fridge,and lights.
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,900
I have an external panel. 8 slots, no main breaker. I will change to a panel with a main breaker. I would like to stay with Square D homeline. I would be using a 5KW generator for emergency use only, so only furnace blower, fridge,and lights.
pics go a long ways
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,275
Location
SE MI
I have an external panel. 8 slots, no main breaker. I will change to a panel with a main breaker. I would like to stay with Square D homeline. I would be using a 5KW generator for emergency use only, so only furnace blower, fridge,and lights.
Good plan ! Use an interlock.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,049
Location
Coronado, CA
Using an Interlock properly is inconvenient and might cause you to stand in inclement weather; if you are so sweet that you might melt in the Rain I guess you would be happier with an Automatic Transfer Switch.

Convenience has a COST.
 
To avoid these ads, REGISTER NOW!
OP
G

gayler

Well-known member
Joined
Sep 22, 2011
Messages
3,282
Location
Lakin Kansas
Using an Interlock properly is inconvenient and might cause you to stand in inclement weather; if you are so sweet that you might melt in the Rain I guess you would be happier with an Automatic Transfer Switch.

Convenience has a COST.
Trust me.I’m not sweet.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,721
Location
Fargo, ND
I have a 200AMP Square D............all circuits are full
I will bet there are some circuits that could share a breaker and open up a couple slots. I have seen individual bedrooms on there own breaker, living rooms and what not generally do not produce much of a load and can share a breaker.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,721
Location
Fargo, ND
A downside to interlocks is that you don't know when the power is back on unless you install a power back alarm, manually check by flipping back to utility power or see lights on at a neighbor that doesn't have a generator
Can not see the neighbor's lights?

Just get a indicator light wired in a the utility side of the main breaker.

If nothing else, walk to the panel and switch of the breaker to the generator, and flip on the main. You should be able to figure it out! :ROFLMAO:
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,073
Location
Modesto, CA
A downside to interlocks is that you don't know when the power is back on unless you install a power back alarm, manually check by flipping back to utility power or see lights on at a neighbor that doesn't have a generator

Setup an alarm that is triggered via an inductive coil around the line side wire on the main breaker

sorry, I had to correct the grammar in the title...
What did I miss?
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,576
Location
Northern Virginia
Transfer switch installation will require you to jerk the meter and rewire your main panel as a subpanel (separate the neutrals and grounds). Depending on your power company, they may or may not let a licensed electrician pull the meter but the power company usually comes back to reinstall the safety seal.

With the interlock, you don't need to jerk the meter or convert your main panel to a sub panel.
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,900
Existing panel

Transfer switch installation will require you to jerk the meter and rewire your main panel as a subpanel (separate the neutrals and grounds). Depending on your power company, they may or may not let a licensed electrician pull the meter but the power company usually comes back to reinstall the safety seal.

With the interlock, you don't need to jerk the meter or convert your main panel to a sub panel.

uhh no? his main panel is in the yard. his house panel is a 100a sub panel. he can kill the breaker in the yard panel, put in a transfer switch for the house and re-energize without power company.
 

White Shadow

Well-known member
Joined
Jan 26, 2014
Messages
985
Tell me about it.....I had to buy TWO automatic transfer switches since my house has 400A service by way of 2 separate 200A runs.
 

Attachments

  • A2AJ.jpg
    A2AJ.jpg
    197.8 KB · Views: 72

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,073
Location
Modesto, CA
Transfer switch installation will require you to jerk the meter and rewire your main panel as a subpanel (separate the neutrals and grounds). Depending on your power company, they may or may not let a licensed electrician pull the meter but the power company usually comes back to reinstall the safety seal.

With the interlock, you don't need to jerk the meter or convert your main panel to a sub panel.
Umm not in all cases

One could install a manual non-service rated transfer switch between main and a subpanel with all critical loads
 

White Shadow

Well-known member
Joined
Jan 26, 2014
Messages
985
why not put a 400a ATS in?

I have two separate 200A panels, so in order for my generator to run the entire house, I need two separate transfer switches. As far as I know, there's no way to have one transfer switch control both panels. And even if there was, how much does a 400A ATS cost?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,920
Location
Richmond, VA
I have two separate 200A panels, so in order for my generator to run the entire house, I need two separate transfer switches. As far as I know, there's no way to have one transfer switch control both panels. And even if there was, how much does a 400A ATS cost?
About 2x the cost of a 200 from what I can see. Roughly 2k vs 1k each

You would have the meter flow directly to the 400a switch then the two panels off of it. But that would also require a new meter pan, I believe, so the separate ats's may be best
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,900
About 2x the cost of a 200 from what I can see. Roughly 2k vs 1k each

You would have the meter flow directly to the 400a switch then the two panels off of it. But that would also require a new meter pan, I believe, so the separate ats's may be best

you can't take 400 from the 400/320 meter pan to a 400a ATS then split coming out of the 400a ATS?


its also a slight increase in redundancy with split 200s. and frankly easier to source anymore. so I get it.
 