I'm installing new electrical service to my garage, and wanted to get some feedback on my approach for the wall penetration. My wall is just PBR panel skin with horizontal steel girts on 2' centers.

Because the steel for the skin is so thin, I will end up with the distance from the back of the meter base to the back of the panel being about 2 inches after I put strut in. This means that I need a method of connection that's lower profile than standard for my 3 3/0 feeders. My current thought is a 2" rigid coupling through the wall penetration, attached to the box knockouts with chase *******. Is this code compliant, and is it a good approach? How have others approached this problem?
 

Attachments

  • Rigid-coupling.png
    Rigid-coupling.png
    49.8 KB · Views: 50
To avoid these ads, REGISTER NOW!
OP
L

lukel99

Member
Joined
May 17, 2021
Messages
23
Location
Richmond, VA
As soon as I posted this, I had a eureka moment.

New plan is to use a 2" rigid conduit ****** in the correct length, lock nuts on either side of the knockout, and bushings to protect the wires where the threads are. Is this considered weatherproof enough for this application?
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
As soon as I posted this, I had a eureka moment.

New plan is to use a 2" rigid conduit ****** in the correct length, lock nuts on either side of the knockout, and bushings to protect the wires where the threads are. Is this considered weatherproof enough for this application?
That is exactly what I was going to suggest
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,013
Location
Modesto, CA
As soon as I posted this, I had a eureka moment.

New plan is to use a 2" rigid conduit ****** in the correct length, lock nuts on either side of the knockout, and bushings to protect the wires where the threads are. Is this considered weatherproof enough for this application?
just make sure its below any live parts such as buss bars
 
To avoid these ads, REGISTER NOW!
OP
L

lukel99

Member
Joined
May 17, 2021
Messages
23
Location
Richmond, VA
TIP! "IF" you are using the concentric knock outs on the panel make sure to use a grounding bushing.
Will do. I didn't realize that conduit grounds are not sufficient in service applications. I've laid a decent amount of EMT for branch circuits, but this is my first service install so I didn't know about the fact that the physical conduit connection is not approved for bonding in service applications. Thanks for pointing me in this direction.