So in another thread I mentioned I got a kiln but it's 208v 3 phase however my garage is 240v single phase. So getting a quote from manufacture to do the proper swap of everything that is needed and it's just under a grand for all the parts.
Someone else mentioned getting a buck boost step down transformer and I have a question on getting the right thing.
Below is the data plate from the kiln. 208v, 3W 2phase, 23.1 amps and 8320 watts. Manufacture suggests a 40 amp breaker (even though the plate says 23.1 amps)
When looking online at buck boost transformers, most of them say Power Rating of x.x kVA and don't mention watts or amps. Is there some conversion from amps or watts to kVA?