Garage GFCI Keeps popping

ps2cho

Well-known member
Joined
Mar 19, 2013
Messages
197
I have a GFCI in the garage, and it keeps popping for some unknown reason. I lost all the food in my garage freezer last week...Got an alarm now so that wont happen again.

Problem is I put a amp reader on the outlet, and nothing is pulling anywhere close to 15amps. My Air Compressor I turned off to be sure it wasn't that, and last night it tripped again. The only things plugged in were some drill batteries and the deep freezer, pulls no more than 2amps.

I have very minimal electrical background. Would you guys suggest I just replace the GFCI outlet entirely first (I should be able to do that with the breaker off). Or is there anything else I should check first?
 
To avoid these ads, REGISTER NOW!

duneslider

Well-known member
Joined
Jan 20, 2013
Messages
2,267
Location
Riverton, Utah
Fridges and freezers generally have a higher amp draw when starting up then drop lower when running. I have had a lot of nuisance trips with older gfci's but don't seem to have much of that issue with newer quality gfci's. I would buy a nice name brand gfci and swap it out and see if it improves. Usually when I have had them go bad though they trip and won't reset.

It could be some leakage current from all the stuff you have plugged in too. You could try leaving everything but the freezer plugged in and see if it stops happening. I was told you really should have dedicated circuits for the fridge/freezer so this doesn't happen. I am not an electrician so I can't intelligently comment on why exactly this is the case but maybe someone else can.
 

bbbarracuda

Well-known member
Joined
Jun 1, 2008
Messages
709
GFCI's will pop for ground faults.
I had one that would pop very intermittently, several days, or a few hours, never knew when it would go.
After much troubleshooting, moving things to other outlets with extension cords, etc., I found an outlet strip was the cause of the problems. After replacing that, it hasn't popped in several months.
So look at everything plugged in to it, and move them one at a time to another outlet to see if problem goes away, or moves to other outlet.
 

bdbecker

ALLIANCE MEMBER
Joined
Nov 18, 2015
Messages
5,582
Location
Iowa
@duneslider summed it up well.

I had the same thing happen - older GFCI in the garage started tripping, but thankfully I didn't lose the contents of my freezer. Other than the garage door opener, the freezer is the only other thing on that circuit that regularly draws power. I swapped it out for a new one and haven't had any issues since. Hopefully the case is the same with you.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,419
Location
VT
This isn't an amperage issue, and gfci outlets don't trip because of excessive current.

Gfci trip due to ground faults. The freezer is likely leaking current to ground.

Is this a GFCI outlet or breaker? I think Breakers have an indicator telling you if it was a over current or ground fault trip.
 

Big Bad Dad

Well-known member
Joined
Jan 31, 2010
Messages
2,664
Location
Southwest/ Central Va.
This isn't an amperage issue, and gfci outlets don't trip because of excessive current.

Gfci trip due to ground faults. The freezer is likely leaking current to ground.
I cannot really agree. My small air compressor for nail guns would trip the GFCI in my house if I was trying to run it when it was very cold and pulling a lot of current. No problem at all when the compressor was warm. I also had a problem once with the refrigerator in my garage popping the GFCI receptacle. (Lucky, no food was involved, I just had warm beer.) I replaced the GFCI, and the problem kept happening. Pulled the 'frig out and found the airflow through the bottom and condensor was partially blocked and restricted by dirt, debris, spider webs, and general bug type ****. Cleaned it out, and all was well again. I think the blockage was causing the compressor or fan to draw more current.
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,048
I have a GFCI in the garage, and it keeps popping for some unknown reason. I lost all the food in my garage freezer last week...Got an alarm now so that wont happen again.

Problem is I put a amp reader on the outlet, and nothing is pulling anywhere close to 15amps. My Air Compressor I turned off to be sure it wasn't that, and last night it tripped again. The only things plugged in were some drill batteries and the deep freezer, pulls no more than 2amps.

I have very minimal electrical background. Would you guys suggest I just replace the GFCI outlet entirely first (I should be able to do that with the breaker off). Or is there anything else I should check first?

GFCI's will pop for ground faults.
I had one that would pop very intermittently, several days, or a few hours, never knew when it would go.
After much troubleshooting, moving things to other outlets with extension cords, etc., I found an outlet strip was the cause of the problems. After replacing that, it hasn't popped in several months.
So look at everything plugged in to it, and move them one at a time to another outlet to see if problem goes away, or moves to other outlet.
GFCIs don't actually detect ground faults, they detect imbalance between L/N. over 4mA and they're supposed to trip. sometimes they fail, sometimes you have a problem to fix, and many of them hate HF noise.
 

Captain Spaulding

Well-known member
Joined
Feb 13, 2017
Messages
754
Location
Southern Indiana
I cannot really agree. My small air compressor for nail guns would trip the GFCI in my house if I was trying to run it when it was very cold and pulling a lot of current. No problem at all when the compressor was warm. I also had a problem once with the refrigerator in my garage popping the GFCI receptacle. (Lucky, no food was involved, I just had warm beer.) I replaced the GFCI, and the problem kept happening. Pulled the 'frig out and found the airflow through the bottom and condensor was partially blocked and restricted by dirt, debris, spider webs, and general bug type ****. Cleaned it out, and all was well again. I think the blockage was causing the compressor or fan to draw more current.
120V GFCIs trip for only current imbalance between hot and neutral. Never for excess current. They don’t even attempt to measure the current flowing through them.

Startup surges on some motor driven appliances can cause a temporary current imbalance and result in tripping. Refrigerators and freezers are notorious for this.
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,048
I think the 5-15R units only switch the hot, not the neutral.
1663779880214.png
 
Last edited:

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,041
Location
Coronado, CA
All of my food storage freezers and refrigerators are on Non GFC! dedicated circuits. I did that because when I was teaching Electrical Wiring i learned that the permissible leakage current in the heating element for a self defrosting Freezer or Refrigerator was sufficient to trip a GFCI.

The receptacles are singe, not duplex, and are high on the wall to avoid them being mistakenly confused as a general purpose receptacle.
 

duneslider

Well-known member
Joined
Jan 20, 2013
Messages
2,267
Location
Riverton, Utah
Are dedicated non-gfci even permissible in garages currently? I know in the past you could have dedicated non-gfci with a label indicating it but I thought I had heard that was no longer acceptable? I thought I had heard that even ALL outlets in basements have to be gfci now?
 

CharlieCA

New member
Joined
Dec 31, 2010
Messages
2
Any chance you have mice? I had garage arc fault / ground fault breaker tripping every so often. Then it tripped permanently. Found first outlet, disconnected rest or the downstream outlets. No trip. Repeated until I found where one outlet worked, next one didn't. Between these two outlets, romex went up through header, across garage attic, back down through other end header. I found chewed wire going through the header.

Found where they were getting in. Had to rip out some drywall and wall insulation. Fixed entry, trapped mice over a couple weeks, and replaced the damaged romex run.

Hopefully not a critter issue.

But process of starting at first outlet and working your way along the run is still likely the best approach to find the issue.
 

KenC

Well-known member
Joined
Dec 20, 2009
Messages
2,594
Location
oklahoma
Self defrosting ref/freezers often have unacceptable leakage in the heating circuit. I'd remove the GFCI if it were mine as long as it is a dedicated circuit. Barring that, maybe remove the heater and do without the self-defrost feature.
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,048
Self defrosting ref/freezers often have unacceptable leakage in the heating circuit. I'd remove the GFCI if it were mine as long as it is a dedicated circuit. Barring that, maybe remove the heater and do without the self-defrost feature.
makes you wonder why they don't put in better insulated heaters, eh?
 

buzzworth

Well-known member
Joined
Oct 22, 2007
Messages
936
Location
Louisville, KY
My septic tank pump did the same thing. I would have the alarm go off every now and then and the time it went off at 2 AM was the last straw. I removed the GFCI on the dedicated line.
 
To avoid these ads, REGISTER NOW!

jkuro

Well-known member
Joined
Apr 28, 2009
Messages
552
If your GFCI is going bad, you will get nuisance tripping. Common problem with older GFCI's.
 

CraigStu

Well-known member
Joined
May 22, 2014
Messages
4,053
Location
Blacksburg, Va
First step is replace the GFCI outlet. They are about $20 so not a huge hit. Be VERY careful about getting the correct wire to the correct lug on the new outlet. They are not all arranged the same so moving a wire from the right top lug on the old one to the right top on the new one doesn't always work. Also spend time finding every other outlet that is on that ones circuit. In the last house we had the exhaust fan over the MBR shower go out once in a while (every 3-6 months). It popped the GFCI in the hall way bathroom. I replaced the GFCI, the wall switch in both bathrooms, and the fan assembly and it kept doing it. One day we plugged something in to the outdoor outlet at the deck and it didn't work. Trying to figure out which breaker it was on I found that it fed off of the GFCI that was always popping. Main floor deck outlet fed off 2nd floor GFCI. Took it apart and it was corroded like crazy. Replaced it and sealed the outlet box better. Dang builders saved $15 by not using two GFCI outlets and cost me 2 years and about $200.
 

PelicanPines

ALLIANCE MEMBER
Joined
Apr 30, 2014
Messages
38,130
Location
New Jersey, USA, Earth, My own reality
My garage gfci had outlets on the load end... One was outside... got wet... constantly tripped the gfci. Installed a non gfci dedicated outlet for my freezer. It also has a temp display that mimics that value on my inside freezer display.
 

Grant Gunderson

Well-known member
Joined
May 17, 2013
Messages
2,330
Location
Bellingham, WA
Had an issue with the garage gfci, then realized it was tripping due to an outside outlet that was powering a fountain pump that went bad. So it’s important to remember a gfci outlet can control a whole circuit, but just it’s outlet.
 

mikedodge

Well-known member
Joined
Jun 27, 2017
Messages
2,839
Replace it with a normal plug and avoid the future risk of food going bad.
GFCI's can be picky about certain motor loads but you don't hear as much about that anymore. They've been improved over the years.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
All of my food storage freezers and refrigerators are on Non GFC! dedicated circuits. I did that because when I was teaching Electrical Wiring i learned that the permissible leakage current in the heating element for a self defrosting Freezer or Refrigerator was sufficient to trip a GFCI.

The receptacles are singe, not duplex, and are high on the wall to avoid them being mistakenly confused as a general purpose receptacle.
At one time that was permitted to have a non GFCI protected receptacle for a dedicated appliance, not anymore.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,041
Location
Coronado, CA
At one time that was permitted to have a non GFCI protected receptacle for a dedicated appliance, not anymore.
To the best of my recollection, the non GFCI receptacles were installed when it was permissible, I ave owned and lived in this house continuously since 1988.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
To the best of my recollection, the non GFCI receptacles were installed when it was permissible, I ave owned and lived in this house continuously since 1988.
I was not saying your situation is good/bad, as did not have a clue when it was done, only that it was once okay.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,611
Location
BC
Self defrosting ref/freezers often have acceptable leakage in the heating circuit.
FIFY. Older units often had trace leakage current because they never anticipated their use on a gfci circuits.

I don't and won't use gfci in my garage or with fridges freezers. Weren't required for the first 25 years of my life and I'm not starting now.
 

p00p

Well-known member
Joined
Nov 23, 2019
Messages
1,997
Location
42.4974° N, 82.8964° W
I've got one that thunder or a low jet will cause it to pop off. Even happens with nothing on the circuit. Replaced it twice and have learned to live with it.
If all the items being plugged in, using that circuit are 100% fault free, check that entire circuit over for a loose screw, sloppy wire nut, chattering ground wire. An instructor once demonstrated how a loose connection can cause a fire if not corrected. It was also found that a loose wire typically develops if the wire material is aluminum or when serrated hardware should not be repurposed.
 

p00p

Well-known member
Joined
Nov 23, 2019
Messages
1,997
Location
42.4974° N, 82.8964° W
Are dedicated non-gfci even permissible in garages currently? I know in the past you could have dedicated non-gfci with a label indicating it but I thought I had heard that was no longer acceptable? I thought I had heard that even ALL outlets in basements have to be gfci now?
Last I knew; My local code allows non GFCI's in an attached garage if the wall that it is in, is an interior wall. Detached might be a whole different ball of wax, since it would be a standalone building & (in theory) burning itself down in to the ground if something went awry.
 

kaffine

Well-known member
Joined
Dec 13, 2009
Messages
3,610
Location
Henderson, NV
Last I knew; My local code allows non GFCI's in an attached garage if the wall that it is in, is an interior wall. Detached might be a whole different ball of wax, since it would be a standalone building & (in theory) burning itself down in to the ground if something went awry.

GFCI are not made to prevent fires they are made to prevent electrocutions.
 

John in OH

Well-known member
Joined
Jun 2, 2007
Messages
2,444
Location
SE Ohio & Eastern Virginia
I guess I'm still not clear on what type of GFI the OP is using. If it is a GFI BREAKER in the breaker box, then it will trip on either over-amperage or ground fault. If it is a GFI OUTLET ( with multiple associated sub-outlets ) then it will trip on ground fault only. The OP needs to clarify what he actually has (or maybe he did and I missed it!!).
 

red61cj5

Well-known member
Joined
Mar 31, 2016
Messages
3,755
Location
West Virginia
Garage refrigerators are often old house fridges that the wife wanted replaced (at least that's my case). Older units often play hell with GFI receptacles. I just made a dedicated non gfi receptacle, which solved my warm beer problem. Will I die by electrocution? Possible, I suppose, but realistically there's about a million other ways that are more likely. My morning commute, for instance.
 

JRC3

Well-known member
Joined
Jun 30, 2014
Messages
12,481
Location
Southwestern OH
As Said, replace it, maybe even go 20A. GFCIs are pretty compex and the electronics do fail over time.

IME, it's often caused by something on the load like other outside outlets or lights, as someone else said. More often it's a post light. Too often the direct burial wire gets nicked or cut by landscapers, irrigation, cable, etc and is either unknown, or a shoddy half-assed repair is made. Then, when it rains or whatever, intermittent problems arise.
 