Single-wide feed from building with its own service

Joemctag

Well-known member
Joined
Aug 11, 2017
Messages
813
Location
Outside raleigh nc
Bought 5 acres rural with a farmhouse with a service (meter) and a 10-yr-old metal building with its own service, 200A.
I plan to set up a used, 14 x 70 mobile home near the building ( less than 100’). Temporary ( 3-5 years) while deciding to fix up farmhouse or build new.
The mobile home’s panel is 200A.
Can I feed the mobile home from the building, and if so, what’s the best way?
 
To avoid these ads, REGISTER NOW!

Mzungu

Well-known member
Joined
Sep 3, 2022
Messages
176
Yes, its no problem to feed the mobile home from the sub panel in your metal building. However, it has to be done in a permanent manner, as there is no provision for temporary in the code that I am aware of regarding your situation. Check your loads in the mobile, does it have an electric furnace, as a 200 amp service is otherwise quite large.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Yep, no problem. It turns out, there is even a wire type called "mobile home feeder", or MHF. 2-2-2-4 is common, which will provide you with up to 90a. What loads will you have in the mobile home? There are larger sizes too, in case you have electric heat or electric hot water.

It's direct Burial so you'll just need conduit above ground.

You'll need two ground rods at the Mobile home, too
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
Bought 5 acres rural with a farmhouse with a service (meter) and a 10-yr-old metal building with its own service, 200A.
I plan to set up a used, 14 x 70 mobile home near the building ( less than 100’). Temporary ( 3-5 years) while deciding to fix up farmhouse or build new.
The mobile home’s panel is 200A.
Can I feed the mobile home from the building, and if so, what’s the best way?
If a single wide trailer has a 200A panel, that would mean to me it's all electric, if it had gas appliances would not need such a large panel, 100A would be sufficient, MH's are built as cheap is possible they are not going to over build the electrical, I cannot see any inspector allowing a smaller service then 200A if the MH has 200A.
 

Mzungu

Well-known member
Joined
Sep 3, 2022
Messages
176
If a single wide trailer has a 200A panel, that would mean to me it's all electric, if it had gas appliances would not need such a large panel, 100A would be sufficient, MH's are built as cheap is possible they are not going to over build the electrical, I cannot see any inspector allowing a smaller service then 200A if the MH has 200A.
Depends, a lot of mobile homes are custom ordered. The previous owner could have requested an upgraded 200 amp service for any number of reasons, one of which includes having significant electric heating load. OP needs to give more load details.
 
OP
J

Joemctag

Well-known member
Joined
Aug 11, 2017
Messages
813
Location
Outside raleigh nc
Yes. It’s all electric. I guess I could put a propane fireplace, the good, modern ones use outside air for combustion.
Question was more like, do I need a disconnect or anything outside the m.h.? Just splice the MHF to the old, cut feed coming down from the m.h. panel in a large j box?
 
OP
J

Joemctag

Well-known member
Joined
Aug 11, 2017
Messages
813
Location
Outside raleigh nc
I’m looking at the NEC “4-wire to DETCHED building” schematic.
So, my m.h.’s panel would now be a sub panel?
Says disconnect means required at nearest entry point.
A suitable disconnect mounted to a 4x4 p.t. post just outside the outer wall of the m.h.?
And try to be prominent so it could be found in an emergency?
 
OP
J

Joemctag

Well-known member
Joined
Aug 11, 2017
Messages
813
Location
Outside raleigh nc
The m.h. isn’t disconnected at its old location (neighbor’s) yet. I guess I want them to leave all the cable going to their old present disconnect/meter ; as long as possible, in other words. So that it reaches my new disconnect with no need to splice?
 

Mzungu

Well-known member
Joined
Sep 3, 2022
Messages
176
I'm working off the Canadian code, but the main breaker in your MH's panel is normally classified as a main disconnect and shouldn't need another one in front of it other than the breaker that will be feeding it from your source. Maybe your local jurisdiction has additional requirements for an exterior disconnect. Not sure on your electric rates there, but those electric furnaces really dig deep into the pocket during the colder months.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Yes the trailer's panel is now a sub. Needs to have the bonding screw removed and all neutrals and grounds separated, plus two rods.

As long as the wire feeding it now is 4 wire, and it's rated for indoor use, you can run it to your current panel or splice onto it
 
OP
J

Joemctag

Well-known member
Joined
Aug 11, 2017
Messages
813
Location
Outside raleigh nc
I'm working off the Canadian code, but the main breaker in your MH's panel is normally classified as a main disconnect and shouldn't need another one in front of it other than the breaker that will be feeding it from your source. Maybe your local jurisdiction has additional requirements for an exterior disconnect. Not sure on your electric rates there, but those electric furnaces really dig deep into the pocket during the colder months.
Yes, I’m sure. And what’s even worse is that the power company is an electric co-op and electric he electricity’s a lot more expensive than I’m used to. Probably will go with the gas fireplace. Will be using it at least 2 years.
 
OP
J

Joemctag

Well-known member
Joined
Aug 11, 2017
Messages
813
Location
Outside raleigh nc
I’m looking at the NEC diagram again and there are a lot of things I’m seeing that I need to check, like the separate, not connected, neutral bar and equipment grounding bar in the m.h.’s panel.
Guess I should take the cover off and take a picture.
 

Mzungu

Well-known member
Joined
Sep 3, 2022
Messages
176
Yes, I’m sure. And what’s even worse is that the power company is an electric co-op and electric he electricity’s a lot more expensive than I’m used to. Probably will go with the gas fireplace. Will be using it at least 2 years.
I feel your future pain, the house I am in has a 20KW furnace, and a wife who likes temperatures above 75. I have added a woodstove and recently a mini split on the upper and lower level. I'm also in climate zone 6 which can have some pretty cold temps.
 
OP
J

Joemctag

Well-known member
Joined
Aug 11, 2017
Messages
813
Location
Outside raleigh nc
Yes the trailer's panel is now a sub. Needs to have the bonding screw removed and all neutrals and grounds separated, plus two rods.

As long as the wire feeding it now is 4 wire, and it's rated for indoor use, you can run it to your current panel or splice onto it
Not even sure it IS 4-wire. 20 years old. I need to verify.
 
OP
J

Joemctag

Well-known member
Joined
Aug 11, 2017
Messages
813
Location
Outside raleigh nc
Just to explain: It’d be great if I had an electrician I trusted to figure all this out. I’ll be doing the buried MHF and mounting disconnect myself, at a minimum. Just want to confirm what any electrician I hire might be saying.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Just to explain: It’d be great if I had an electrician I trusted to figure all this out. I’ll be doing the buried MHF and mounting disconnect myself, at a minimum. Just want to confirm what any electrician I hire might be saying.
We can help you through it, just need details. Wire type, pics of the inside of the panel in the trailer and the one that is feeding this. Stuff like that.

Is this site also in NC? If so, you are on 2020 NEC
 
OP
J

Joemctag

Well-known member
Joined
Aug 11, 2017
Messages
813
Location
Outside raleigh nc
We can help you through it, just need details. Wire type, pics of the inside of the panel in the trailer and the one that is feeding this. Stuff like that.

Is this site also in NC? If so, you are on 2020 NEC
I’m going to get pics, it it’ll be tonight or tomorrow. Thanks for your help.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
I’m looking at the NEC “4-wire to DETCHED building” schematic.
So, my m.h.’s panel would now be a sub panel?
Says disconnect means required at nearest entry point.
A suitable disconnect mounted to a 4x4 p.t. post just outside the outer wall of the m.h.?
And try to be prominent so it could be found in an emergency?
A trailer panel has always been treated like a subpanel, a enclosed breaker & grounding electrodes will to be provided at the back of the trailer, a simple junction box will not cut it. Another solution is either upgrade the existing 200A, service to 400A, or if the PoCo is agreeable set a pole with a 200A service by the trailer & connect it there.
 

Mzungu

Well-known member
Joined
Sep 3, 2022
Messages
176
A trailer panel has always been treated like a subpanel, a enclosed breaker & grounding electrodes will to be provided at the back of the trailer, a simple junction box will not cut it. Another solution is either upgrade the existing 200A, service to 400A, or if the PoCo is agreeable set a pole with a 200A service by the trailer & connect it there.
Maybe when it's in a trailer park with a rented pad, but on private land its common to see them with the meter mounted on the side just like any other house.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,245
Location
Modesto, CA
A trailer panel has always been treated like a subpanel, a enclosed breaker & grounding electrodes will to be provided at the back of the trailer, a simple junction box will not cut it. Another solution is either upgrade the existing 200A, service to 400A, or if the PoCo is agreeable set a pole with a 200A service by the trailer & connect it there.
ive seen some that were not set up like that
 
OP
J

Joemctag

Well-known member
Joined
Aug 11, 2017
Messages
813
Location
Outside raleigh nc
Got pics but will have to learn how to post.
The MH panel is a Cutler-Hammer. Four ********* wires and a somewhat smaller green coming in. My questions so far are:
Will I need a disconnect ? Just outside the MH where my feed is coming up ? Can I go to an electrical supply and they’ll give me the right one. Code says something about stickers ( for identification in an emergency).
Code says I need ground rod(s) at MH. What’s the easiest way to do this. Sand for a couple feet, then clay.
Also, the building I want to feed from has a meter on the exterior but not a disconnect there.
I guess the first, biggest question is whether I can feed a 200A MH panel ( will become a sub panel) from a 200A panel in the building.
What if I put a gas furnace or fireplace insert to eliminate the present electric furnace, thereby not needing anywhere near 200A?
Would that entail getting a lesser-amperage panel?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,245
Location
Modesto, CA
Got pics but will have to learn how to post.
The MH panel is a Cutler-Hammer. Four ********* wires and a somewhat smaller green coming in. My questions so far are:
Will I need a disconnect ? Just outside the MH where my feed is coming up ? Can I go to an electrical supply and they’ll give me the right one. Code says something about stickers ( for identification in an emergency).
Code says I need ground rod(s) at MH. What’s the easiest way to do this. Sand for a couple feet, then clay.
Also, the building I want to feed from has a meter on the exterior but not a disconnect there.
I guess the first, biggest question is whether I can feed a 200A MH panel ( will become a sub panel) from a 200A panel in the building.
What if I put a gas furnace or fireplace insert to eliminate the present electric furnace, thereby not needing anywhere near 200A?
Would that entail getting a lesser-amperage panel?
are you sure its 4 and not 3? should only be 3 plus the green ground.

As to connecting to connecting to the building with the meter, is there a breaker panel on the inside?
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,132
Location
Central Iowa
There's probably a bare #4 going down that used to go to the rods, or it goes to a ground bar mounted to the frame with an additional hole or another lug that went to the rods. Or, it could just be cut off and hanging there.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,642
Location
BC
IMHO, the practical thing to do is put the largest breaker in the metal building's 200A panel that it allows - likely 100-125A - and feed that to the mobile.

It is doubtful this would fly with a permit unless you crippled the mobile's electric heating (and whatever else) to arrive at a load calc that would fly on the 100-125A breaker.

While it's more work, you may be able to redo the metal building's service gear to allow 150-175A thru to the mobile. I doubt you will be able to get the full 200A though, because the metal building will need a base amount (its own load calc.) This is also contingent the metal building has a full 200A in the first place.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,245
Location
Modesto, CA
IMHO, the practical thing to do is put the largest breaker in the metal building's 200A panel that it allows - likely 100-125A - and feed that to the mobile.

It is doubtful this would fly with a permit unless you crippled the mobile's electric heating (and whatever else) to arrive at a load calc that would fly on the 100-125A breaker.

While it's more work, you may be able to redo the metal building's service gear to allow 150-175A thru to the mobile. I doubt you will be able to get the full 200A though, because the metal building will need a base amount (its own load calc.) This is also contingent the metal building has a full 200A in the first place.
There is no code that would prohibit breakering the MH feeder at 200a
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,642
Location
BC
There is no code that would prohibit breakering the MH feeder at 200a
Ya, I can't speak for NEC directly.... I know i had to reel it in on a previous job because the AHJ cited the shop demand took away from what could carry on to the house. Ymmv.
 
OP
J

Joemctag

Well-known member
Joined
Aug 11, 2017
Messages
813
Location
Outside raleigh nc
Ya, I can't speak for NEC directly.... I know i had to reel it in on a previous job because the AHJ cited the shop demand took away from what could carry on to the house. Ymmv.
Thanks, you all! I now have the professional opinions of some electricians who work to the NEC every day, so I’ve got a pretty good picture of where things stand and what all the options are.
 