Probably overthinking it but still curious about voltage drop on long runs inside a large shop, or even a big azz house.
Wiring a 16x30 wood framed room inside a 42x54 metal building.
Panel is located in front corner outside of the framed room.
I pulled four 120v circuits from the panel in conduit under the slab to the back wall where I’ll locate a junction box. About 70’ of wire. THWN #12.
Due to the layout I’m now heading back where I came from. LOL
From the j box another ~8’ along a wall girt and then entering the framed room. I’m feeding 8 outlets total on both sides of the wall between the framed room and the shop.
By the time I reach the last outlet inside the room that’s another 30’. So we have a circuit with ~110’ of #12.
When I look at voltage drop tables it appears a problem could arise, depending on load.
How or when might there be a problem using typical 120v power tools? Miter saw, band saw, sanders, routers, etc.
Very unlikely more than one tool would be in use at the same time and I’m also staggering the outlets between two circuits on that wall.
This is all dependent on load isn’t it?
Thanks
Wiring a 16x30 wood framed room inside a 42x54 metal building.
Panel is located in front corner outside of the framed room.
I pulled four 120v circuits from the panel in conduit under the slab to the back wall where I’ll locate a junction box. About 70’ of wire. THWN #12.
Due to the layout I’m now heading back where I came from. LOL
From the j box another ~8’ along a wall girt and then entering the framed room. I’m feeding 8 outlets total on both sides of the wall between the framed room and the shop.
By the time I reach the last outlet inside the room that’s another 30’. So we have a circuit with ~110’ of #12.
When I look at voltage drop tables it appears a problem could arise, depending on load.
How or when might there be a problem using typical 120v power tools? Miter saw, band saw, sanders, routers, etc.
Very unlikely more than one tool would be in use at the same time and I’m also staggering the outlets between two circuits on that wall.
This is all dependent on load isn’t it?
Thanks