Garage wiring advise

Poppypop04

Member
Joined
Nov 15, 2022
Messages
19
Looking to wire up my new 22x25 metal garage and I think I'm going to run a 60a double pole from my outside house box to a 125a garage panel, it's only about a 15ft run of wire buried). Question though. Can I use well pump wire instead of thhn run in conduit? I have a 100ft or so of 10/3 submersible wire that I would think would work great.? Only looking to power about 4 led lights, air compressor and occasionally use of a mig welder.
My dad gave me some 1/0 aluminum that I would use but I have no idea how to connect the wire in my main panel(too big) .
 
Last edited:
To avoid these ads, REGISTER NOW!

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,267
Location
Penngrove, California
No. Do not use cord for any type of permanent installation. Do not breaker any form of 10 ga wire with a 60 Amp breaker. Best to install a sub panel and feed with proper gauge wire like 4 gauge copper.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,023
Location
Modesto, CA
Looking to wire up my new 22x25 metal garage and I think I'm going to run a 60a double pole from my outside house box to a 125a garage panel, it's only about a 15ft run of wire buried). Question though. Can I use well pump wire instead of thhn run in conduit? I have a 100ft or so of 10/3 submersible wire that I would think would work great.? Only looking to power about 4 led lights, air compressor and occasionally use of a mig welder.
My dad gave me some 2awg aluminum that I would use but I have no idea how to connect the wire in my main panel.
is it 4-wire or 3-wire? what type of insulation does it have? (post a pic of the label on the cable)

regardless, #10 is too small for a 60a feeder

what type of #2 AL is it? have a pic of the label?
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,597
Location
BC
Does #2 not fit in your 60A breaker?

If not, get a bigger one that does.... Up to 90A max for that wire.
 

Red 17

Well-known member
Joined
Oct 25, 2018
Messages
441
Location
Pasadena CA
Go bigger, 60A is too small. You may not be thinking this now, but if you end up with any kind of electric vehicle, you will need a 50A circuit to charge it. Ask the man who knows about his 60A garage.......

Or at least add another 2" conduit and cap it off if you don't want to go bigger now.
 
OP
P

Poppypop04

Member
Joined
Nov 15, 2022
Messages
19
Does #2 not fit in your 60A breaker?

If not, get a bigger one that does.... Up to 90A max for that wire.
Had to correct my initial post, but it's actually 1/0 service wire that he gave me. Unless there is a way to reduce the size down to fit the 60a feed breaker and 125a box I'll have to use some other wire.
 
OP
P

Poppypop04

Member
Joined
Nov 15, 2022
Messages
19
Go bigger, 60A is too small. You may not be thinking this now, but if you end up with any kind of electric vehicle, you will need a 50A circuit to charge it. Ask the man who knows about his 60A garage.......

Or at least add another 2" conduit and cap it off if you don't want to go bigger now.
So what size feed breaker do you recommend?
 
OP
P

Poppypop04

Member
Joined
Nov 15, 2022
Messages
19
Ok so :
60a feed breaker in main panel, either 2-2-2-4 mhfw, or possibly #6 and is this panel box ok?
Screenshot_20221123_230222_Chrome.jpg
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,758
What brand, or do you have a link maybe to one?
Anything except Eaton BR, or GE, stay away from the BR in particular. Eaton CH, SQ D QO, or HOM, Siemens are all OK, although using the same manufacturer as your house panel is best.
 

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
I don't see Murray mentioned very much, but the supply house right down the street from work has their stuff. I'm not about to add anything to my mix (QO/HOM at my house, CH at my dad's) but what's the prevailing opinion here on Murray?
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,758
I don't see Murray mentioned very much, but the supply house right down the street from work has their stuff. I'm not about to add anything to my mix (QO/HOM at my house, CH at my dad's) but what's the prevailing opinion here on Murray?
Murray is no more, Siemens discontinued them a few years ago.
 

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,325
Location
Alexandria, VA
I haven't researched wire prices in a while, but 2-2-2-4 AL MHF that was dual rated (burial or conduit) used to win out for cost/amps most of the time. Its good for up to 90 amps, but works fine with an easy-to-find 60 amp breaker in the main panel. Use a 100 amp subpanel with a main breaker and at least 12 circuits and you have a very versatile setup.

It should be run it in conduit anywhere its in a building or exposed, and that is usually required to comply with code. I also prefer conduit when buried, but its not required for MHF if its buried at the proper depth. You can also use a junction box to transition from 4 wire MHF to 4 wire SER cable once you are inside the dwelling, and SER does not require conduit in the building.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,036
Location
VT
QO or HOM? I recommend sticking to whatever is existing.
I never understood this recommendation.

What circumstances occur where I absolutely need to steal a breaker out of my other panel immediately?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,599
Location
Richmond, VA
I never understood this recommendation.

What circumstances occur where I absolutely need to steal a breaker out of my other panel immediately?
I agree. I can't come up with a situation. If the breaker for your fridge dies, swap it from any other circuit in the same panel. Most people have no need to keep spare breakers on hand
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,036
Location
VT
I agree. I can't come up with a situation. If the breaker for your fridge dies, swap it from any other circuit in the same panel. Most people have no need to keep spare breakers on hand

Most people will need to call an electrician.

Hell, I'd just run an extension cord until I could get to a store.
 

Wiz02

Well-known member
Joined
Jul 13, 2007
Messages
2,399
Location
Southeastern PA
I never understood this recommendation.

What circumstances occur where I absolutely need to steal a breaker out of my other panel immediately?

Well here's a scenario, my home has a heat pump, with electric resistance heat for backup. I had a new heat pump installed when the old compressor died, but I switched to an LP gas furnace for emergency heat. I removed the 2 pole 60 amp breaker that fed the old resistance coils and will be using it for my 240V air compressor in the garage, because I went with the same CH breakers when I wired the garage.

Admittedly it's not a compelling use case, but I only have to stock a single breaker style.
 

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
I'm sticking with the same brand for my dad's house because I can re-use some breakers.

I split away and went HOM for my own sub (QO main) because I had a few of those breakers already and the PON stuff was really easy.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,599
Location
Richmond, VA
I'm sticking with the same brand for my dad's house because I can re-use some breakers.

I split away and went HOM for my own sub (QO main) because I had a few of those breakers already and the PON stuff was really easy.
Not sure on your circumstances, but IMO, if there is enough reason to replace a load center everything in it should be trashed too unless it was recently installed.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,758
I never understood this recommendation.

What circumstances occur where I absolutely need to steal a breaker out of my other panel immediately?
Because it's moronic to put in a hodgepodge of panels, unless the existing is obsolete.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,599
Location
Richmond, VA
Because it's moronic to put in a hodgepodge of panels, unless the existing is obsolete.
Two brands on a property is hardly a hodgepodge. Besides what practical benefit does interchangeability give? No one is swapping breakers around between panels.

I have two homelines and a Siemens. Partly because the Siemens is what was available, partly because it just doesnt matter
 

ddurrett896

Well-known member
Joined
Mar 29, 2015
Messages
995
Location
VA
That short of a run, I’d do 100amp to detached with a standard panel (with disconnect).
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,597
Location
BC
Two brands on a property is hardly a hodgepodge. Besides what practical benefit does interchangeability give? No one is swapping breakers around between panels.
I sure am... :LOL:
My own stuff is never done and always changing, so one brand/type is ideal.

A contractor doesn't care because they simply buy whatever a job requires and walk away at the end.
 
OP
P

Poppypop04

Member
Joined
Nov 15, 2022
Messages
19
Ok so following up on some things.
I've got some 2-2-2-4 and my 100 amp service panel and I'm almost ready to run the wire. I had to add a ground bar to my new panel but have a few questions.
Being such a short run of 10 ft do I really need the additional 2 ground rods?
Also I'm attaching a pic of my outdoor main panel with an illustration of what I think I need to do, but please correct me if I'm wrong.
 

Attachments

  • 20221119_160700.jpg
    20221119_160700.jpg
    1 MB · Views: 46

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,599
Location
Richmond, VA
If it is in a detached structure, the rods are required. Your wiring proposal looks fine for a main panel since that is the only place neutrals and grounds can be connected
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,778
Location
Austin, TX
Two brands on a property is hardly a hodgepodge. Besides what practical benefit does interchangeability give? No one is swapping breakers around between panels.
I have 2 "mains" off a split meter.
The house currently has 5 panels.
The shop has 5 panels.
ATS, generator, and solar, and RV panels... So you end up with a lot of electrical. We've expanded the shop twice.

Sounds excessive, but quite a few of these panels are Siemens Talon panels that have the receptacles that I use commonly - they allow future expand-ability downstream.

I absolutely have moved breakers around and reconfigured things over the years... There's a big advantage for me to keep all the breaker types the same.. I have a box of spare dual pole breakers as well as 20A single poles.
 