Beacon Morris BRT-045 Not Working

ErickForest

Well-known member
Joined
Sep 17, 2008
Messages
174
Location
Minnesota
I have a Beacon Morris BRT-045 heater that will not ignite. I have replaced the gas valve, tried a new ignitor and have tested the pressure switch and will still not ignite. The only other thing I can think of is the control board. Part of the control board is discolored by some resistors. Thinking that could be the problem. The heater seems to fire some times but will only run for about 30 seconds. Wondering if others have experienced issues with control boards or if it could be something else. The vent fan is loud, but it has always been that way. I have read where it could possibly be the vent fan, but that seems unlikely to me. Just was looking for advice if I should just replace the control board for $265 or try something else.
 
To avoid these ads, REGISTER NOW!

gmcgeo

Well-known member
Joined
Mar 11, 2019
Messages
3,701
Throwing parts at it is a waist of money, testing gas pressure before and after the gas valve. Then testing the vent, and if it has a pressure switch.

See if there is codes being thrown.

need to start testing, then fix the problem
 

jmarkwolf

Well-known member
Joined
Jan 15, 2013
Messages
1,812
Location
Southeast Michigan
I know this is an old thread but my Beacon Morris BRT-045 heater just failed after 12 years.

Had a local HVAC contractor out to look at it, and all he found was the 24volt circuit read just 16V until he wiggled some wires. This contractor doesn't work on Beacon Morris heaters so he didn't want to dig into it any further, they deal in reznor heaters.

I asked him to generate a quote for replacing it with a Reznor. Having a heater that the local HVAC can service has it's appeal. We'll see.

I bought it pretty reasonably IIRC at Menards 12 years ago, hung it myself, and had a service install the gas line and B-stack.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,625
Location
Fargo, ND
Had a local HVAC contractor out to look at it, and all he found was the 24volt circuit read just 16V until he wiggled some wires. This contractor doesn't work on Beacon Morris heaters so he didn't want to dig into it any further, they deal in reznor heaters.
What kind of service tech won't work on something they didn't sell? Seems like the new, current line of contractors that all they want to do is sell. That Beacon Morris probably has a wiring diagram on the service access and more than likely has very similar function to a Reznor.

Unless you are really wanting it replaced, I would call someone else, or maybe call someone else any way.
 
Last edited:
To avoid these ads, REGISTER NOW!

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,888
What kind of service tech won't work on something they didn't sell? Seems like the new, current line of contractors that all the want to do is sell. That Beacon Morris probably has a wiring diagram on the service access and more than likely has very similar function to a Reznor.

Unless you are really wanting it replaced, I would call someone else, or maybe call someone else any way.

@jmarkwolf this. Any 'service' person who can't fix a unit heater, or at least tell you why it can't or shouldn't be fixed, isn't a service tech, they're a salesman, at best. Unit heaters are pretty simple, it should have a wiring diagram on the door, and anyone who knows how to use a meter should be able to diagnose it.

Even if you want to replace it, get it done by someone who isn't going to try and sell you things you don't need, just because you didn't buy it from them.
 

finn

Well-known member
Joined
Mar 27, 2005
Messages
16,209
Location
The UP, God's country
I have a couple of them. Mine still work. There was a tech line phone number in the owner’s manual. I think I called them for some reason, but that was years ago.

From what I recall, they produced heaters under a couple of brand names.. They’re based in Massachusetts, and have a phone number listed on their web page.
 

ripperd

Well-known member
Joined
Jul 2, 2014
Messages
2,044
Location
Twin Cities, MN
If you replace it, you are going to be on the hook for replacing the B-vent with cat 3 stainless as well. That will up the price a bit (but make it less prone to the exhaust corroding out).
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,968
Location
Peace Valley,mo
Probably has a bad board tech wiggle a wire and then he had proper power. Loose terminal or bad solder joint on the board. Wouldn't repair the board because of the liability if something else would fail wouldn't be on the hook. Have found a lot of 1/4" push on terminals bad overheated or cracked.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,888
Probably has a bad board tech wiggle a wire and then he had proper power. Loose terminal or bad solder joint on the board. Wouldn't repair the board because of the liability if something else would fail wouldn't be on the hook. Have found a lot of 1/4" push on terminals bad overheated or cracked.
Maybe, but the guy should be able to say “needs a new board, probably should buy a new one from me.”

If so, it’s probably obvious under visible inspection, and could be an easy fix.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,933
Location
Coronado, CA
If the magic smoke that is installed in every electrical and electronic part of your equipment at the factory leaks out you are guaranteed to have a problem. Those problems can only be corrected by the replacement of parts that come with the factory installed smoke.
 

jmarkwolf

Well-known member
Joined
Jan 15, 2013
Messages
1,812
Location
Southeast Michigan
What kind of service tech won't work on something they didn't sell? Seems like the new, current line of contractors that all they want to do is sell. That Beacon Morris probably has a wiring diagram on the service access and more than likely has very similar function to a Reznor.

Unless you are really wanting it replaced, I would call someone else, or maybe call someone else any way.
I did indeed call someone else and there' testing was much more comprehensive.

He cleaned the sensors found a loose wire and noticed some heat induced discoloration on the board around some power resistors, that the first guy apparently overlooked. He cycled the power and the NG numerous times, and it appeared to be fixed, but he said if it failed again that it's time for a new controller board, and that there would be no additional service call fee, just the cost of the board. It only lasted a few hours and failed again.

He came back the next day and installed the board and it's been working fine since.

During the down time I called around for numerous quotes to replace the heater with a new 45,000 BTU unit heater, and they ranged between $2800 and $5500 installed. I was under the impression that regulations had tightened and that homeowners could no longer buy their own NG heaters, but this is not true. I had installed the original Beacon-Morris 45,000 BTU 12 years ago myself except for running the black pipe from the meter and installing the flu stack, and I'll be doing it again next time. I'll buy another of the same model and the stack and black pipe should be a snap to hook back up.
 
Last edited:

finn

Well-known member
Joined
Mar 27, 2005
Messages
16,209
Location
The UP, God's country
The Beacon Morris units are pretty well constructed compared to the units that superseded them at Menards.

I’ve been using a couple for about 10 or 12 years now in different buildings. I’m not running them full time, though.
 