Not an electrician here, excuse if it has been discussed also. Quincy says a #10 wire with a 40 amp breaker. al I have read for the last week is 10/2 or 8/2 wire and 30 amp breaker. Can someone please let me know what number wire and breaker to use? thhn, nm-b or? Thanks you for your input. It's a 5 hp and 21 amp draw.
 
To avoid these ads, REGISTER NOW!

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,271
Location
Coastal NJ
A 30A circuit requires a 10ga wire almost always. Looks like you have a dedicated circuit for a compressor that runs at 21A. The motor startup current will be higher. Hence the 40A breaker is specified. As long as the compressor is the only load on that circuit, all is well.
 

Rinspeed

Well-known member
Joined
Apr 26, 2020
Messages
1,832
Location
NY
I think 10 GA with a 30 AMP breaker should be fine but you have to remember that the start-up amperage with the 10-15% fudge factor might put you slightly over 30A. The only way to be sure is to measure it.
 

71goldss

Well-known member
Joined
May 23, 2012
Messages
1,513
Location
Northern Calif
I’ve been running my Quincy QT-54, with Baldor motor on a 30A breaker and 10ga wire for ten years now. No problems here.
 
To avoid these ads, REGISTER NOW!

Augus7us

Well-known member
Joined
Jan 14, 2017
Messages
1,190
Location
Central Ohio
You can run them on a 30amp but its not code. As others pointed out the surge when it starts is what the breaker is for.

I think i ran 6-2 for my qt5.
 

71goldss

Well-known member
Joined
May 23, 2012
Messages
1,513
Location
Northern Calif
You can run them on a 30amp but its not code. As others pointed out the surge when it starts is what the breaker is for.

I think i ran 6-2 for my qt5.
My 30amp breaker has never tripped on start up. I’m not an electrician, but should I have other concerns other than not code? If I’m not mistaken, I believe 10 years ago when purchasing my QT-54, the recommended breaker was 30amp. This was one of the reasons I chose this compressor, since I already had a 30amp source in my garage.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,768
Location
Richmond, VA
I think 10 GA with a 30 AMP breaker should be fine but you have to remember that the start-up amperage with the 10-15% fudge factor might put you slightly over 30A. The only way to be sure is to measure it.
FYI, startup current is way more than 10-15%. 4-6x running current (so 80-120 amps) is more typical, but it's fast enough to not pop the recommended breaker
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,271
Location
Coastal NJ
You can run them on a 30amp but its not code. As others pointed out the surge when it starts is what the breaker is for.

I think i ran 6-2 for my qt5.
You sure it's not to code? This is a dedicated branch circuit. It's a very specific code section.

Conductors are sized to 125% of the motor run current. 21A X 125% = 26.25A
The correct conductor for that is 10ga.
The overcurrent (short circuit) protection, commonly knows as the breaker is sized to accommodate the startup current.
Quincy says use 40A breaker.
This meets code.

Now if this was a non-dedicated general purpose branch circuit let's say with a receptacle, a 10ga wire would be limited to 30A breaker.

You will find even larger discrepancies with welders. 10ga wire and 50A breakers etc.

 
Last edited: