How many lights can you put on a 20A circuit? I will have 6 2'x4' 4 bulb fixtures, 2 ceiling fans, and the 2 outside lights. My questions is, can I run that on one circuit or will I need 2? I guessing 2 but I want to ask the pro's.

Thanks in advance,
Gary
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Depends on how big the outside lights are but generally these could be ran on a single circuit but often the choice is somewhat a matter of convenience of being able to work on one circuit without having to disable the other.
 

Random Guy

Well-known member
Joined
Jun 16, 2009
Messages
155
I'd recommend running them off of two circuits, just so in the event one of the breakers trips, you are not left in total darkness.
 
OP
G

gmhill33

Well-known member
Joined
Oct 5, 2009
Messages
539
Location
Ohio
Depends on how big the outside lights are but generally these could be ran on a single circuit but often the choice is somewhat a matter of convenience of being able to work on one circuit without having to disable the other.

Thanks for the reply. One of the outsides lights is just a single bulb light fixture beside a entry door (probably with a sensor). The other is a going to be some kind of light (with a sensor) so when we pull in the driveway it will come on.

Thanks,
Gary
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Sometimes the routing with a couple circuits makes it easier to add things at a later date. If I had the panel spaces the main cost is an additional breaker, maybe a few feet of wire, neither that big of deal. In my own case I have several circuits with only one duplex on them, wire right straight from breaker to outlet.
 
Last edited:

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Lighting is considered a continuous load under the NEC, and continuous loads cannot exceed 80% of a circuit or device's rated capacity. Thus a 15 amp circuit is limited to 12 amps max load and a 20 amp circuit is limited to 16 amps in this situation (and a good rule to follow in any situation, not just continuous loads).

Look at your lighting devices, the ID tags on them will have the total load of the fixture or device, add these up and as long as they do not exceed 12 amps or 16 amps, depending on the circuit, you are OK.

Random Guy makes a good point of separating the circuits however, and that is a good policy to follow also.

Charles
 
Last edited:
To avoid these ads, REGISTER NOW!

p_mori7

Well-known member
Joined
Mar 23, 2010
Messages
3,340
Location
Montreal, QC., Canada
Amps = Watts / Volts

so...

if you were to run 10 x 100W bulbs, the constant draw on that circuit would be 9.0A

10 x 100W = 1000W / 110V = 9.0A

20A circuits require 12GA wiring (in Canada anyways)
 
Last edited:

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,774
Amps = Watts / Volts

so...

if you were to run 10 x 100W bulbs, the constant draw on that circuit would be 9.0A

10 x 100W = 1000W / 110V = 9.0A

20A circuits require 12GA wiring (in Canada anyways)

110V should NEVER be used to calculate circuits,since it does not exist as a supply voltage.
 

p_mori7

Well-known member
Joined
Mar 23, 2010
Messages
3,340
Location
Montreal, QC., Canada
The rule still applies, the higher the voltage, the lower the amps.

10 x 100W bulbs = 1000W / 120V = 8.3A

Of course, if the Amperage is listed on the doodad your hooking up to the circuit, it makes it a lot easier...
 
Last edited:

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
The rule still applies, the higher the voltage, the lower the amps.

10 x 100W bulbs = 1000W / 120V = 8.3A

Of course, if the Amperage is listed on the doodad your hooking up to the circuit, it makes it a lot easier...

As I noted earlier, that works with incandescent lighting, but not with other types of lighting. I have Metal Halide lighting, which is ballasted. The bulbs are "400 watt" and marked that way, yet 400/120 is 3.33 amps, yet, if you read the data plate, or measure the draw with a clamp amp meter, they draw 4.0 amps. Fluorescent lighting works the same way, however with the new electronic ballast the calculated and actual draws are very close, while with the older magnetic ballast the actual and calculated draws are much further apart.