Another wire feed to new shop question

ixlr8

Well-known member
Joined
Sep 15, 2009
Messages
438
Location
Eastern Shore Virginia
I have a 4 bay garage which has 200 amp service to it. I am building a storage/workshop building and I want to get power from the garage to the workshop. The panel in the garage is in the back corner from where the workshop is. I am planning for 100 amp service in the workshop. It will take about 30 ft of wire to get from the garage panel to the outside of the garage and then about 110 ft from the garage to the panel in the workshop. With a fudge factor, let's call it 150 ft total. What size wire do I need and is there a wire that can be run from panel to panel, or will I need to transition to different wire types inside the building vs what is going to be buried? I ask as when I had my dock wired, they used one type of wire in the house, then a junction box and then another type of wire buried to the dock. I would think there is one type of wire that could run the distance without a junction box for transition between types.

TIA
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,245
Location
Modesto, CA
first off, what loads will you have in the workshop, how many people will be working in there etc?

to answer your question about wire, there is only a few types of wire that will allow you to go panel to panel. XHHW and THWN, which require conduit panel to panel and MHF/mobile home feeder, which requires conduit indoors; conduit recommended panel to panel.

doubtful that you need 100a but if you do, #1 al should suit you fine, even with voltage drop.

EDIT: post edited to include forgotten wire types
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
first off, what loads will you have in the workshop, how many people will be working in there etc?

to answer your question about wire, there is only 1 type of wire that will allow you to go panel to panel, but it requires conduit indoors. its called mobile home feeder.

doubtful that you need 100a but if you do, #1 al should suit you fine, even with voltage drop.
I know you know there's more than just MHF. There's also XHHW-2 or THWN in conduit panel to panel.
 
OP
I

ixlr8

Well-known member
Joined
Sep 15, 2009
Messages
438
Location
Eastern Shore Virginia
There will only be one person working in the shop. I think the highest load at any given time will be my welder. My present welder requires either a 20 amp 120 connection or a 30amp 240 connection, but if I ever want to upgrade then it would go to a 50amp 240 connection. To be honest I don't know if I will ever really need to upgrade my welder. It might be more prudent to tack things together with my present welder and give it to a pro to finish if I need some heavy duty welding. I will have table saw, belt sander, planer/joiner, grinder, 120v lift, compressor, etc, but only running one at a time. Really being honest I suspect a 60-75 amp service would be more than enough. Heck in my previous shop I ran everything with a 120 volt extension cord running 100ft from my house for 2 years until I could get it properly wired. It just meant that I ran my welder on 120, which wasn't the best. I just want to make sure I future proof so I don't find myself going oops I don't have enough power. I guess the biggest question is, would I ever need to install an EV charger. With a bit of reflecting, I suspect a 60 amp service would be more than enough.
 
OP
I

ixlr8

Well-known member
Joined
Sep 15, 2009
Messages
438
Location
Eastern Shore Virginia
Thanks for all your input. Wylies hope you feel better soon. Sounds like MHF is the way to go. I just need to put it in conduit inside the buildings. Since it will be crossing under the driveway to the garage, I suspect it would be best to put it in conduit all the way. I can save about $60 getting the 2-2-4-6 mhf vs 2-2-2-4 mhf. Is there any issue going with the 2-2-4-6, or since it is only a $60 difference, just get the 2-2-2-4?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Thanks for all your input. Wylies hope you feel better soon. Sounds like MHF is the way to go. I just need to put it in conduit inside the buildings. Since it will be crossing under the driveway to the garage, I suspect it would be best to put it in conduit all the way. I can save about $60 getting the 2-2-4-6 mhf vs 2-2-2-4 mhf. Is there any issue going with the 2-2-4-6, or since it is only a $60 difference, just get the 2-2-2-4?
Either are fine. The reduced neutral would take effort to pose a problem

Make sure you use conduit everywhere above ground, at a minimum. Conduit everywhere is not a bad idea
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
If doing conduit from panel to panel you don’t need a direct bury cable so you should check the price of XHHW-2. MHF being direct bury has heavier insulation making it a little stiffer to work with, also being a twisted assembly makes it stiffer.
 
OP
I

ixlr8

Well-known member
Joined
Sep 15, 2009
Messages
438
Location
Eastern Shore Virginia
XHHW-2 is cheaper, thanks for the advice. Interesting, I priced #2 AL at various Home Depots and found the price for a 500ft roll varied between $258 and $486 depending on which store I looked at!!!
 
To avoid these ads, REGISTER NOW!

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,908
Location
Southern Oregon
It will take about 30 ft of wire to get from the garage panel to the outside of the garage and then about 110 ft from the garage to the panel in the workshop.
You may have already accounted for it, but don't forget the vertical path component.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,131
Location
Central Iowa
XHHW-2 is cheaper, thanks for the advice. Interesting, I priced #2 AL at various Home Depots and found the price for a 500ft roll varied between $258 and $486 depending on which store I looked at!!!
If you go that route, make sure to account for the price of the PVC before pulling the trigger on the XHHW. The retailers have gotten pretty proud of it, the box stores are blowing the supply houses away price wise and a 110' underground run is going to be a whole lot more than it should be.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
Either are fine. The reduced neutral would take effort to pose a problem

Make sure you use conduit everywhere above ground, at a minimum. Conduit everywhere is not a bad idea
I agree about conduit, & like to oversize for a easier pull, but 2" SCH 40 PVC is $3 a ft at HD.
Depends on service size, 6 or 8, minimum.

I'd just run 6, or 4 if the price wasn't wild
No matter what size service the conductor to the rods does not need to be larger then 6 AWG, using 8 AWG will trigger needing protection from physical damage.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,131
Location
Central Iowa
Sure.

Or if you have extra #4 from running it to your water line.

Either way, I am not arguing that #6 is sufficient
One AHJ has an amendment that we have to use #4 because of those pesky weed eaters. I just use #4 for everything since it's easier to keep track of one roll.
 
OP
I

ixlr8

Well-known member
Joined
Sep 15, 2009
Messages
438
Location
Eastern Shore Virginia
If you go that route, make sure to account for the price of the PVC before pulling the trigger on the XHHW. The retailers have gotten pretty proud of it, the box stores are blowing the supply houses away price wise and a 110' underground run is going to be a whole lot more than it should be.
Local Lowes wants $25/10ft stick and local supply house wants $37/10ft stick. Since the wire is running under a gravel driveway I think for long term safety I am going to run conduit for the entire route. My electrician recommended using 1-1/2" conduit, should I upsize that to 2"?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Local Lowes wants $25/10ft stick and local supply house wants $37/10ft stick. Since the wire is running under a gravel driveway I think for long term safety I am going to run conduit for the entire route. My electrician recommended using 1-1/2" conduit, should I upsize that to 2"?
When you pull, you won't ever wish you went smaller. That said, if you keep the bends to a minimum, #2 will get through 1.5" just fine.

Eliminating fittings where possible helps a lot. Don't just trench perfectly straight lines and use fittings to change direction. Try to make bends sweeping and just bend the conduit to conform. A heat gun can help a lot too
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,131
Location
Central Iowa
Local Lowes wants $25/10ft stick and local supply house wants $37/10ft stick. Since the wire is running under a gravel driveway I think for long term safety I am going to run conduit for the entire route. My electrician recommended using 1-1/2" conduit, should I upsize that to 2"?

1-1/2 will be fine. Plenty of people are going to tell you 2" at a minimum, but that's a waste
 