    Reznor unit hetater issu(s)

    I fired heater up this morning.... no more gas valve clicking :unsure:.... taking that as a good sign though unsure why it went away. At this point though I'm feeling as if problem(s) solved. Thanks everyone for chiming in.... couldn't have done it without you!
  2. B

    Reznor unit hetater issu(s)

    Thanks!!! I'll try adjusting the pilot up tomorrow.
  3. B

    Reznor unit hetater issu(s)

    After over an hour the valve clicking seems to have stopped. The fan is still short cycling but the warmer it gets in the building the longer the run cycles get. The temp is hovering near 50 deg. and I've shut it down for today.
  4. B

    Reznor unit hetater issu(s)

    Made some headway but still having other issues. Replaced the pilot ignition assembly and heater fired immediately, so that problem seems to have been sorted out. But now, with heater running, the gas valve keeps clicking every few seconds (wasn't doing that before or at least not as frequently...
  5. B

    Reznor unit hetater issu(s)

    No, it 45's right off the flue into a straight run out thru the wall. Tomorrow I will check for the cracks you mention. And thanks for the manual!
  6. B

    Reznor unit hetater issu(s)

    Thanks.... DONE!
  7. B

    Reznor unit hetater issu(s)

    But it lights just fine when dropped out of the burner box. That's what I don't get.
  8. B

    Reznor unit hetater issu(s)

    I'm not sure what you mean by that.
  9. B

    Reznor unit hetater issu(s)

    hmmm... wondering how I might make that adjustment. Did you bend something towards the hood?
  10. B

    Reznor unit hetater issu(s)

    It mostly arcs across to the thermocouple. It occasionally jumps to the pilot hood, and sometimes between both at the same time. But in general it's almost always to the thermocouple whether the unit is installed or just hanging loose underneath when it almost always light immediately. I haven't...
  11. B

    Reznor unit hetater issu(s)

    This appears to be the ignition/pilot module that is on my pre-2014 Reznor. I need to remove grille over fan in order to clearly see serial #. I did remove the pilot tube but there doesn't appear to be a ferrule, the end of the tube seems to be attached to what appears to be cylinder about the...
  12. B

    Reznor unit hetater issu(s)

    I hung a Reznor FE-200 (200,000 btu) unit heater in an ag building recently. It's supplied by NG and supposedly worked when uninstalled previously before I got it. It sat around for a couple years before I got around to hanging it. Fan motor was slightly stuck, but easily returned to function...