Thank you for the response concerning the breaker size.
The compressor is 15 feet from the breaker box.
My concern is looking at the connections would size 8 wire fit in these openings indicated in the inserted picture or would I need to attach a spade connector (if that is an option) like in...
Yes... I do understand it needs to be hard wired... Just wasn't sure if the 8 gauge wire would fit but in the connection to the compressor.
Sent from my Pixel 2 using Tapatalk
Harbor Freight 93274 Compressor.
Honestly I have never ran 220V but have installed 110V circuits and I have a question concerning wire size.
The manual says 40 amp breaker...This should require 8 gauge wire from what I have read.
My question is will 8 gauge wire fit in these connections?
Also...
I have attached pictures of the trusses in my shop. I need to lift a 500 lb compressor off of the back of a pickup truck. Thinking about using chain horse on the truss to lift. Think it would be able to take that much weight on one side of the truss? Thanks
Sent from my XT1585 using Tapatalk
I looked into the vfd... However from what I understand I would need a three phase rotary converter which is pretty expensive.
Sent from my XT1585 using Tapatalk
I recently acquired a industrial 60 gallon IMC air compressor. However it has a 3 phase motor instead of single phase. I have attached a picture of the plate on the motor.
I want to replace this motor with a single phase... The three phase 5hp shows 1740 rpm and I noticed the single phase 5hp...
Here is link to pic after cleaning with detergent. I guess I need to get some more muriatic acid.
Any suggestions.
http://imgur.com/a/Ijsxb
Sent from my SCH-I545 using Tapatalk