Wiring Air compressor
medic502
South Carolina
Harbor Freight 93274 Compressor.
Honestly I have never ran 220V but have installed 110V circuits and I have a question concerning wire size.
The manual says 40 amp breaker...This should require 8 gauge wire from what I have read.
My question is will 8 gauge wire fit in these connections?
Also my box already has a 50 amp breaker that came with it... Could I use this 50 amp breaker instead of the 40?
Thanks for the Help.efbebf674195ead605e4131e560d1dfd.jpg061c560afec67186bcb5a3a9cf1aeed2.jpgb032dfe178374b22d650425a163d3e0b.jpg
Sent from my Pixel 2 using Tapatalk
sberry
Brethren, Michigan
Doesnt look like any reason that the 50 wouldnt work. The breaker isnt really per wire size like it would be for a general circuit with multiple recepts on it. In some cases a 50 breaker could be used with 12 wire.
I will have to give HF a couple of points here for trying to be helpful for including some general wiring instructions. They gave a lay version, there is a range of breakers that would work. It needs 8 wire if its cable, 10 individual conductors in pipe.
medic502
South Carolina
Yes... I do understand it needs to be hard wired... Just wasn't sure if the 8 gauge wire would fit but in the connection to the compressor.
Thats a 5HP compressor so you need #8/2 NM-b or #10 THWN in pipe.
If compressor is not within sight of and further than 50' away from breaker panel then you need a disconnect.
Breaker can be max 250% of FLC which is 35a for 5HP but 50a breaker should be fine if you already have that.
medic502
South Carolina
Thank you for the response concerning the breaker size.
The compressor is 15 feet from the breaker box.
My concern is looking at the connections would size 8 wire fit in these openings indicated in the inserted picture or would I need to attach a spade connector (if that is an option) like in the factory connections also in the picture. fb058dcf15cb08c6f37c03f66964a087.jpg
Habrot
Clifton,New Jersey
Without seeing the inside of the motor, and tracing the wires from the coils and switches, etc, it's at best difficult to guess about the terminals; there's no convention that I know of.
pattenp
Virginia - USA
Norcal
You need to use flex conduit to the compressor from the wall. Should not use NM-b. You can use #8/2 NM-b from panel to box on wall and step down in size to a #10 A/C whip from box to compressor.
I think this is convenient to use as a jbox plus it gives you a switch at the compressor,
https://www.homedepot.com/p/Square-...kW-Non-Fuse-AC-Disconnect-QO200TRCP/202353314
here's a A/C whip.. https://www.homedepot.com/p/Southwi...t A/C disco, much cheaper and easier to wire.
Norcal
I am a wire nut fan, not adding a piece more than I need in this type of circuit.
The NEC is a minimum standard and I would rather have the disco close then walk some distance to shut it off when servicing it, and pullout type discos are cheap.
Citation
Indy
This compressor's pressure switch appears to include an on/off function like many 120v compressors. Assuming the circuit panel was say more than 50ft away does it still need a local wall switch/disconnect? I had always assumed that rule applied to compressors that had no built in power switch (ie no power switch as part of the pressure switch or mag starter).
a pressure switch with on/auto-off function does not count as a disconnect. nor does a switch that is part of the mag starter relay wiring.
And if its more than 50' away it needs a disconnect. The disconnect is for servicing.
Citation
Indy
I didn't realize that. The two hardwired compressors I've helped with were both within feet of the panel so this wasn't an issue.
What counts as a disconnect? I'm assuming it must disconnect both L1 and L2. Does it need to have a positive disconnection? For example, when I look on HD's website I see things like a 30 A double pole "light switch"
https://www.homedepot.com/p/Leviton...ble-Pole-Switch-White-R62-03032-2WS/100356941
Assuming the 30A rating was sufficient for a 15A motor, would that count or does it need some way to prevent easy reactivation? How does the code view that switch vs this pull type disconnect
https://www.homedepot.com/p/GE-60-A...on-Metallic-AC-Disconnect-TPN60R1CP/100569466
or this safety switch?
https://www.homedepot.com/p/GE-30-A...PIPHorizontal3_rr-_-305904198-_-202978650-_-N
I'm asking out of interest. I've done a decent amount of electrical work but most at the electronics level where a mistake burns of a micro or shorts your power supply. Less in the CAT 3 and above land hence why I ask.
What are the rules for the disconnect? Does it have to be a double throw? I don't know if that is the correct electricians term but I'm thinking like a double pole switch where both L1 and L2 would be disconnected at the same time. From a pure schematic POV I would consider a disconnect like this a STDP switch since it opens/closes two connections at once.
PT Doc
Disconnects must be motor rated. If you go by amps only then you can have issues. Similarly a 50 amp plug is not rated for a 5 hp motor but the 50 amp breaker would cover amp requirements of the 5 hp motor.
PT Doc
Look at Leviton motor rated disconnects. For example, MS602 is a single phase 60 amp disconnect. MS603 is a three phase 60 amp disconnect.