Recent content by Mx391

  1. M

    100 amp, not 90

    I got 10ft of 1-1-1-4 SER to go from house panel to junction box in the crawl space. Then I got #1 AL xhhw to go from inside junction box, through the conduit into the shop panel. Thanks for the info guys!
  2. M

    100 amp, not 90

    Thanks for the info!I already installed both ground rods. They are 8ft apart. Really tough to pound into the hard as rock TN dirt! I used a #6 ground wire from panel to ground rods.
  3. M

    100 amp, not 90

    Exactly my thoughts. A little extra wont hurt. I've already went over my budget, whats a little more :lol_hitti
  4. M

    100 amp, not 90

    I was worried about a #1 AL fitting inside the breaker. Shouldn't have any problems?
  5. M

    100 amp, not 90

    Im ok with copper or AL, I just wanting 100 amps, not 90.
  6. M

    100 amp, not 90

    Yes I know another 100 amp sub panel thread :eyecrazy: Seems like everytime someone asks, it always derails into "just do 90 amp breaker with 2-2-2-4 AL. Well I want to feed my sub panel with a 100 amp breaker, not a 90. I've got access to a code book, but it's way too confusing for me to...
  7. M

    Underground conduit into crawlspace

    That's exactly what I'm gonna have to do. Can you post pics how you mounted your junction box?
  8. M

    Underground conduit into crawlspace

    I've got cinder block foundation right under my home panel. I would have to break up 2 or 3ft of cinder block. Don't want to do that. Wish I could figure out how to post pics off my phone.
  9. M

    Underground conduit into crawlspace

    I can run conduit through the crawlspace, but I cant 90 up into the house panel without major demo.
  10. M

    Underground conduit into crawlspace

    Good idea on the junction box. Thanks!
  11. M

    Underground conduit into crawlspace

    100 amp breaker
  12. M

    Underground conduit into crawlspace

    Ive got a 100 amp sub panel in my pole barn, 33ft from my house. I'm running 2" PVC 2ft underground from my crawlspace to the shop. There is absolutely no way to run 2" conduit into the house panel(feeder panel). So I'm thinking I will have to go from the feeder panel, along bottom of floor...
  13. M

    Third time's the charm - 40*50*12 build

    Your entire shop is ran off of an 80 amp circuit correct?
  14. M

    Excavate for concrete after building is finished or before?

    I just had my building built recently. Currently digging out to do gravel and concrete. Wish I would have done it before.