Getting ready to start running electrical to shop equipment and wondering if MWBC are allowed or are a bad idea? In one area I have a tire machine(9 amps), balancer(can't check right now but think it's around the same 9 amps), and parts washer(11.9) amps, and then a couple outlets for 5" hand grinder and anything else I might need. I'm just a home shop guy so will never be using them all at the same time. Only time would be using the grinder to clean a rim while the tire machine is spinning. So thinking two 20 amp circuits would be good for this area. Everything is in a row along the wall and sub panel is roughly 30' from the first machine and I will be running conduit and THHN to this area. Is running a MWBC a bad idea to share the neutral? It's not much in cost savings but trying to plan out my conduit runs and wire fill. I have just started the planning so nothing set in stone, but if I figure it out and there is room in the conduit I might be able to run another circuit for something like compressor that is close. Compressor is 240 with F.L.A, of 15 amps so I have had it hooked up with 12 gauge wire and 30 amp breaker, but if I ran it in same conduit then I believe that would be 4 power carrying conductors and need to derate. Starting to get over my head but if I understand the derating thing it says #12 at 90 degrees is 30 amps and for 4-6 conductors, think this is only counting power carrying conductors and not neutrals and grounds? If so then 80% derate would still allow 24 amps?
Sorry for all the rambling but tried to get all the details out. Actual questions are below,
Is a MWBC allowed and would it make sense to do in my situation? Or since it's a short run and I believe I have room in the 3/4" conduit just pull another neutral?
Can I run two 120V/20A circuits or one 240V/20A MWBC in 3/4" conduit and then also run my compressor wiring in there? Think the wire fill would be fine but not sure about the derating part for number of conductors? Thanks
Sorry for all the rambling but tried to get all the details out. Actual questions are below,
Is a MWBC allowed and would it make sense to do in my situation? Or since it's a short run and I believe I have room in the 3/4" conduit just pull another neutral?
Can I run two 120V/20A circuits or one 240V/20A MWBC in 3/4" conduit and then also run my compressor wiring in there? Think the wire fill would be fine but not sure about the derating part for number of conductors? Thanks